Thread: Vent line
09-03-2017, 06:41 PM #1
Vent line
Hi friends,
Would you please let me know in this type of receiver "Surge type" where we should install vent line ?
Sincerely yours.
09-03-2017, 11:57 PM #2
Re: Vent line
I think where you have it, is OK.
Assuming this line is connecting into main compressor discharge line, which I would call a "Balance" line.
10-03-2017, 12:30 AM #3
Re: Vent line
As Ranger says it should vent back to the condenser inlet pipe
10-03-2017, 08:07 AM #4
Re: Vent line
Dear Friends,
Thanks for your help. OK , Why in this type of receiver tanks we can have sub-cool liquid ?
Sincerely yours.
01-05-2017, 11:47 PM #5
Re: Vent line
Saturation is the equilibrium state at the surface of the liquid in the receiver. So should liquid as returned from the condenser be colder than the saturation corresponding to the condensing pressure and the liquid flow to the low side downstream of the receiver be equal to or less than the rate at which the condensers are delivering, the liquid flow will go right past the receiver and remain colder than the apparent saturation temperature.....