If the system drops back down to 15 bar after 10 minutes then 1 of two things are happening.
1) The system sees that there is no load/demand
2) The board is telling the compressor to reduce the frequency of the compressor because something is wrong.

Most likely it's No2 and the first thing to check would be the discharge temp sensor and confirm the transducers.