    Jan 2017
    United Kingdom
    1
    City multi fault
    Hello
    I arrived on site to a newly installed city multi system with 1 x ceiling unit not cooling/heating the unit is working just no cooling or heating is happening.
    Ive wound the lev head off and to no avail.
    The addreses are all correct and the controller par31-maa sees the unit and can changed loavers and shut down the unit.
    All other units work correctly
    If anyone has any advice I would be greatful
    I do need to test the solenoid valve plug but the bc box is in such a terrible place you cannot get to the inside of the box.
    ireland
    1,453
    Re: City multi fault
    Is the unit piped to correct outlet on BC box? Sounds like a piping issue
    Mar 2006
    Lancashire
    1,859
    28
    Check 'A & C' solenoids are energized from the BC box PCB in cooling mode and 'B' is energized in heating mode.
    If you're getting the above, then I'd start looking at the port address setting, it's probably something as simple as incorrect/duplicated ports.
    Marc
    Jan 2017
    Hong Kong
    3
    Quote Originally Posted by Airconessex View Post
    Hello
    I arrived on site to a newly installed city multi Prime English system with 1 x ceiling unit not cooling/heating the unit is working just no cooling or heating is happening.
    thanks for sharing