Re: Daikin UA fault
Take the IR receivers off 2 of the indoor fan coils.
You can only have 1 controller fitted on a twin or triple split
You should only have the indoor/outdoor 1 2 3 cable connected between the outdoor and indoor fancoils and the controller connected to ONLY 1 of the indoor units. Don't connect the P1 P2 terminals between fan coils