Results 1 to 3 of 3
-
31-03-2016, 11:03 AM #1
CH 530 Replace the interface operator
Hi All
I need to replace the interface operator on RTAC 300, bécause the screen is destroyed
by the sun ray ! not cover in place !!
My Question: I can use my service tool techwiew for made this ?
( download the software and affect all LLID Sensor temp and press. EXV etc..)
There are à spécific procedure for replace this interface ?
I use my Techview currently for replace the LLID, but I have never use for this !
Thanks for all information !!
Patrick
-
09-04-2016, 10:09 PM #2
Re: CH 530 Replace the interface operator
If is only the touch screen broken,if you buy a new CH530 you can replace ONLY the touch screen and all the setting will remain and you dont need to use the Techwiew.But if you want to replace the CH530 with the Techview you will need the complete model number,confirm code,and serial number and this you will find in the electrical panel on the left side and it is a simple job. Be careful when you type the complete model number not to mistake zero with letter O.If you use Kestrelview save a complete report first,and in the report you will also find the complete model number,confirm code,and serial number.
Last edited by georgeB; 09-04-2016 at 10:50 PM.
-
10-04-2016, 05:02 AM #3
Re: CH 530 Replace the interface operator
Hi GeorgeB
Thanks for being so helpful!
GrizzlyDespite the High Cost of Living it still remains Popular!