    Talking Daikin FLXS50/RXS50
    Hi Guys,
    Have a prob with a U4 fault on this single unit, have 30vdc coming of outdoor unit comms to earth wire 2vdc of indoor unit.
    Checked drain -all clear, powered down and up no joy.
    Flaps opens and closes on indoor -power 230v ok
    suspect indoor unit pcb, any advice would be welcome
    5,667
    Re: Daikin FLXS50/RXS50
    I would run a temporary single core wire between terminal 3 of the indoor and outdoor units to see if that solved the problem
    Split Croatia
    6,151
    Check that terminal 1 and 2 on indoor and outdoor are correctly wired ( not mixed)!
    Feb 2016
    West Sussex England
    9
    I may be your saviour.
    Is the led lit on the outdoor pcb?
    if not, unplug outdoor fan motor, is it now lit (blinking)
    try the outdoor eev head too,
    had this fault on many daikin units,