    Sep 2010
    Lisboa
    42
    7
    Danfoss EKC 202D1 temperature settings
    I need some help on this danfoss EKC 202D1.
    Its controlling a small freezer unit
    The set-point temperature is -18º
    The R1 seting is diferential is 2
    The R2 setting is max limitation of setpoint -16.5º
    The R3 setting is min limitation of setpoint -18º
    But the freezer is getting temperatures of -30ºc
    its just too much cold i don't know what to do to make the temperature stay in the correct interval.
    Where is the manual
    http://www.ra.danfoss.com/TechnicalI...EKC202_302.pdf
    Can someone give me a help?
    Thks
    Apr 2008
    Southampton, England
    49
    1,023
    Re: Danfoss EKC 202D1 temperature settings
    Is the snowflake symbol lit when unit is too cold (indicating controller/set up error) or snowflake symbol off but unit still cooling meaning output relay stuck on, wiring error, solenoid valve passing, etc?
    C30 set to on so relay acts inversely?
    C01 min on time set to 30 mins so over running after setpoint reached?
    Cheers,
    Andy.
    Split Croatia
    6,151
    Give us all "r" codes and "u" codes as read by you at near -30°C temperature!
    manchester
    5,639
    relay sticking- if cooling led isnt lit- tap it with a screwdriver see if it stops
    Sep 2010
    Lisboa
    42
    7
    Thks
    I will try your solutions.
    Sep 2010
    Lisboa
    42
    7
    The snowflake is blinking, but i have other freezers that are blinking too and no problems.
    I change the controller from one freezer to another one, to rule out problems on the freezer, and the problem is in the controller.
    I copy the parameters from other controller to this one, but noting has change.
    All the R codes :
    R1 : 2
    R2 : -16.5
    R3: -18
    R4: 00
    R5 Cº
    R9 0
    R10 0
    R12 001
    r13 000
    R15 000
    r39 off
    r40 000
    U codes
    U 09 -37.4
    u10 off
    u12 - 32.5
    u13 off
    u16 120 (not on danfoss documents)
    u17 -32.8
    u28 -18
    u37 off
    u56 -32.5
    u57 -32.8
    u58 off
    u59 on
    u60 off
    u81 off
    I film all the menu settings, maybe someone whith more experience can see what im doing wrong.
    https://youtu.be/wUpPgmoaw24
    Aug 2014
    75
    508
    Have you checked that you have the correct sensor type fitted . These controllers can use pt 1000 , off and ntc sensors which is parameter o06 , but check the sensor type itself as it may be the wrong type is the pt1000 is 1000ohms at 0 degC and the Ptc is 1000ohms at 25 deg C
    Sep 2010
    Lisboa
    42
    7
    The sensor is correct, i change the other controller whit other freezer and the problem goes with the controller
    I went to the store and got a new one and the problem is solved.
    Thks
    70
    4,700
    47
    Hi EFCM
    Rep Point Given!
    Because you bothered to update us all!