Originally Posted by
install monkey
are u clipping the comp current on the leads or the incoming power to the outdoor?, did you pressure test with ofn (nitrogen) prior to powering up?
was nitrogen used to purge whilst brazing?
use the dipswitches on the outdoor sw1 to read compressor freq, maybe set sw1,1 on indoor (address pcb) to use the thermistor in the remote controller instead of the return air thermistor. (if its in the conditioned space)