Thread: Chiller YORK YCIV0840 Baseplate
-
06-06-2015, 05:58 AM #1
Chiller YORK YCIV0840 Baseplate
Hello all
chiller York YSIV0840
Faulty pump glycol
The display shows: SUS1 LOCKOUT : HIGH VSD BASEPLATE TEMP.
Please, provide technical support and help
Sincerely, Anatoly
-
06-06-2015, 06:08 AM #2
Re: Chiller YORK YCIV0840 Baseplate
amendment YCIV0840SA50VAB
-
06-06-2015, 06:56 AM #3
Re: Chiller YORK YCIV0840 Baseplate
Hi Anatoly
Is your glycol pump ok? Check glycol level.
Check the cabinet fan or you may have a faulty sensorI love the smell of Ammonia in the morning!
-
06-06-2015, 10:00 AM #4
Re: Chiller YORK YCIV0840 Baseplate
Hi hookster
The pump is faulty.
It was the starting block with a broken pump.
Tell me where the sensor?
What are the terminals connected?
Do I need to manually reset this accident?
-
06-06-2015, 01:10 PM #5
-
06-06-2015, 03:40 PM #6
Re: Chiller YORK YCIV0840 Baseplate
The pump is already engaged may replace a new one
problem
Display Indication Sus1 BLOCK: HIGH TEMPERATURE IRR baseplate.
Removing the accident and where the temperature sensor
-
06-06-2015, 03:41 PM #7
Re: Chiller YORK YCIV0840 Baseplate
amendment SUS1 LOCKOUT : HIGH VSD BASEPLATE TEMP.
-
06-06-2015, 06:30 PM #8
Re: Chiller YORK YCIV0840 Baseplate
"Removing the accident"cannot understand. what is the glycol level? if glycol level is low, base plate temp will go high.
-
06-06-2015, 08:29 PM #9
Re: Chiller YORK YCIV0840 Baseplate
circuit status off
where the temperature sensor is installed
-
20-09-2015, 09:49 PM #10
Re: Chiller YORK YCIV0840 Baseplate
Leave sensor location it is on PCB you can not do anything...... If u replaced Glycol pump just topup glycol.......untill overflow then close cap.