12-02-2015, 08:59 AM #1
UNISAB II - remotely stop/start function over SABCOM OPC Driver
are there anyone on these forums that knows how I can start and stop the compressor over the Sabcom OPC interface (RS2LAN)?
My driver is getting all the information from the UNISAB, but I dont know what parameter that starts/stops the compressors.
I have one parameter that is "Control Mode" but i have problems identifying what the modes are.
Someone here that have any experience on this topic?
12-02-2015, 04:39 PM #2
- Sep 2009
- Iran
- 66
- 674
- 1
- 19
Re: UNISAB II - remotely stop/start function over SABCOM OPC Driver
hi recently I bought 4 sab 128 compressor its control by UNISAB II .
send your mail , I will send the copy of them.
14-02-2015, 06:22 AM #3
Hi, nikern
welcome to RE forums ...
Control mode can be:
STOPPED
MANUAL
AUTO
REMOTE
and all above you can set in ...
SETUP>CONTROL>COMPRESSOR CONTROL>
STOPPED
MANUAL
AUTO
REMOTE
within configuration menu you can set CONTROL ON:
1. Suction pressure
2. Brine (measuring water temperature at evaporator output with external PT100)
3. Discharge pressure
4. Hot water (measuring water temperature at condenser output with external PT 100)
5. Ext. cool ....
6. Ext. heat ...
To setup point 5 and 6 you need to use manual to set up EXTERNAL INPUT SIGNAL
Hope this will help a little ...