Re: Just how warm should air be blowing from fan coil units in heating?
I had this issue once. The fault lay with the chw pipework being operational and actuators opening to flood coils with chilled water. This came to my attention whilst maintaining a rooftop vrf at same site and noticed the chillers running up in mid winter. BMS fault in the end. Tempory fixed by switching off chiller and pumps.Chilled water vs LPHW-!!