07-01-2015, 07:05 PM #1
Spectrum SB 30 full of ***** but running in a vacuum
I am working on a spectrum that has the rear unit disconnected. The unit has a newly rebuilt throttling valve on it and I just charged it. The unit is full of ***** but it is running in a vacuum. The high side pressure is stable around 135psi and the low side is in a vacuum. It is cooling but only at a -7* differential.
07-01-2015, 07:19 PM #2
Re: Spectrum SB 30 full of ***** but running in a vacuum
Is the rebuilt valve working?
07-01-2015, 09:25 PM #3
Drier,txv?
08-01-2015, 05:48 AM #4
check the LLS diode is energised on the relay board(liquid line solenoid) Bottom left corner of board.
If it is, probably TX valve or power head fault
09-01-2015, 09:08 AM #5
your problem most be found in the liquid line, check also if your LP-gauge is correct.
09-01-2015, 11:01 AM #6
- Sep 2009
- Iran
- 66
- 673
- 1
- 19
all suggestion might be right,
what is a your refrigeration gas ? why your hp pressure is a 135 psi
if your using R-22 it should not be less than 180 psi , Min. TX valve works pressure to works and open correctly
10-01-2015, 01:05 AM #7