HVAC design of different temperature zone
Hai friends,
I am looking for a solution to my problem from your people
Currently we were designing a DX Ducted Split unit for a Station which have a temperature zone of 22 , 27 , 30 , 40 deg C and 50 % RH.
We need to cater all the zone through a single system.
How the approach to be to get the right solution
Senthil kumar
-
02-12-2014, 04:31 PM #2
Re: HVAC design of different temperature zone
Is that for 1st Class, 2nd Class, 3rd Class and 4th Class areas
I love the smell of Ammonia in the morning!
-
05-12-2014, 06:02 AM #3
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 674
- Blog Entries
- 1
- Rep Power
- 19
Re: HVAC design of different temperature zone
for each on you need one fan and damper .
fan runs with temp. and sucks air from your splits and push air through damper to your room .
damper should be good seal .
-
05-12-2014, 02:01 PM #4
Re: HVAC design of different temperature zone
If it is a single coil in the main duct run it at 22°C and add reheater coils in the various zones.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
06-12-2014, 04:44 PM #5
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 674
- Blog Entries
- 1
- Rep Power
- 19
Re: HVAC design of different temperature zone
that cost more money ?
first you cool it and then you heat it .
it is better he goes to my way.