good morning guys:
I have a carrier 30HXC260 machine with soft starter has the following alarm me the machine is French and we have no information.
appreciate your opinions!
thank you
-
03-11-2014, 06:32 PM #2
-
03-11-2014, 09:15 PM #3
Re: carrier 30HXC260
sorry!
Alarms are 105 and 205
-
03-11-2014, 10:21 PM #4
Re: carrier 30HXC260
Alarms are Comp A1 & A2 Rotor Blocked, High current as viewed against Must Trip Amps (MTA rating) you can download the manuals from
http://eto.carrier.com/lit.asp
-
03-11-2014, 10:41 PM #5
Re: carrier 30HXC260
that can cause these alarms?
damage to the electric motor?
loaded compressor starts?
-
07-11-2014, 10:52 PM #6
Re: carrier 30HXC260
good afternoon:
I have a detail with a high pressure transducer:
at atmospheric pressure, the display indicates when it should be 160kpa 0kPa!
was placed brand new one and 450kpa!
that could be causing this problem?