Results 1 to 15 of 15
    Nov 2005
    kankroli
    30
    R12 based systems to R22or R134a system
    We are having domestic window acs and refrigerators working with R12 as refrigerant. How can I convert the same system to one which can work with R22 or R134A
    Sep 2003
    ISRAEL
    72
    4,248
    Re: R12 based systems to R22or R134a system
    Hi Dilip sahasrabu.
    To convert it to R 22, you will need a smaller compressor with the same capacity.
    The condenser will be too small though.
    Using r 134a, you will have to replace the compressor and clean the system from all oil residues.
    The units you refer to, are very old and inefficient.
    Wouldn't it be wiser to replace them with modern R 410?
    Chemi
    Mar 2004
    Denmark
    65
    Hi Chemi
    What is the problem of using a R12 Compressor to R134A
    if the oil in the compressor is changed. ? and the system
    has been cleaned up as you said.
    Best regards
    Carlo Hansen
    Oct 2005
    IRAN
    878
    Thumbs up Re: R12 based systems to R22or R134a system
    Quote Originally Posted by Carlo Hansen
    Hi Chemi
    Best regards
    Carlo Hansen
    Hi there,
    You can use the same compressor but the capacity will be lower.
    In order to replace R12 with R134a the following procedure must be carefully followed:
    1- Drain the system mineral oil.
    2- Put appropriate synthetic oil in to the compressor.
    3- Turn on the compressor and let it operate for a few minutes.
    4- Turn off the compressor and drain the contaminated oil from the crankcase.
    5- Again put new synthetic oil into the crankcase.
    6- Turn on the compressor and let it operate for a few minutes.
    7-Turn off the compressor and drain the contaminated oil from the crankcase. Test the oil for contamination with special test kit. If the contamination is less than 1% then you can recover R12 from th system.
    8- If oil contamination is more than 1% then repeat from step4.
    9- Change filter/drier,TEV, ...
    10- Evacuate the system and change the oil again.
    11- NOW YOU CAN CHARGE R134a.
    Remember if the oil contamination is more than 1% then you can not charge R134a.
    The synthetic oil is very hygroscopic i.e., absorbs moisture, be very careful.
    I hope this helps a bit.
    Even Einstein Asked Questions
    Dec 2004
    Australia
    52
    519
    Quote Originally Posted by lana
    Hi there,
    G'day lana
    By the time you have done all this wouldnt it be cheaper to buy a new unit?
    If it was a billable job to a customer they would be better off spending their money on a new system with warranty.
    Unfortunately we are becoming a throw away society.
    Sep 2005
    Singapore
    145
    Quote Originally Posted by Temprite
    G'day lana
    Agree, unless it is a 1000 RT Centrifugal chiller.
    Nov 2005
    152
    We don't give out D I Y advice to homeowners i hope !
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
    Mar 2004
    Denmark
    65
    Hi Fridg;
    Velcome to this forum.
    (We don't give out D I Y advice to homeowners i hope !)
    I would like to know what you mean by this ?
    Thx. Lana for the description of convert from R12 to R134A
    This is what i have learn many eyars ago. In the meantime
    it is normaly just to remain the oil to 5% in the system.
    The main reason to reduce the oil to 1%, was to eleminate copper to atack the valves in the compressor.
    Best regards
    Carlo Hansen
    Sep 2003
    ISRAEL
    72
    4,248
    Hi Carlo,
    As you said, no problems at all, it is exactly the same inside the compressor and only oil changing and a quick system clean will do the job just fine.
    a small window AC unit, is very simple, I agree.
    Chemi
    Apr 2001
    Southern England
    66
    123
    Just be aware that dropping R22 into an elderly R12 system is like putting a turbo on your mums 20 year old Ford escort at best it will leak like a sieve and die rapidly. At worst you will be pulling little bits of metal from your customers body......check your pressure tables....
    CFC to HFC conversions (R12 to R134a) rarely suceed. The gaskets and seals go first followed by the compressor. Every brazed joint will develop a hole....
    Then we have R11 to R123 conversions......
    In any conversion remember to check the max working pressure of your system and validity all of the safety cutouts.
    Derek
    Nov 2005
    152
    [QUOTE=Carlo Hansen]Hi Fridg;
    Thanks Carlo. I love this trade , i am a 2nd year apprentice.
    We don't give out repair techniques to people who are not in the trade or not studying the trade do we ?
    Just with all the new laws and dangers involved in this industry , i would hate to see someones advice land them in a civil suit.
    And on the other side i would hate to see a poor hvac system suffer.
    Remember the oil
    this will have to be changed
    at least.
    Nov 2005
    152
    Quote Originally Posted by dogma
    Hey Fridg. Knew you'd get here pretty quick. Joined up last month. See you round the way.
    Roger that tango !
    We seem to find each other in the most unusual places
    Jun 2005
    U.K.
    Quote Originally Posted by Dilip sahasrabu
    hi
    over here in the uk we get away by using an drop in refrigerant like R409a this seem to work ok here.
    Augustine's Avatar
    Augustine Guest
    You cheap ****, stop bothering engineers
    with your chep ideas.
    Buy a new fridge!!
    Nov 2005
    kankroli
    30
    Can anybody tell me about the Capillary size changes required in case of retrofitting from R-12 to R-134a? Is there any online chart for the same?
  1. Daikin fault codes
  2. System Burn Out Troubleshooting
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Last Post: 23-03-2010, 12:39 PM
  4. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  5. LonWorks based control systems
    By Randy S. in forum New Technologies
    Last Post: 06-05-2001, 04:08 PM