Results 1 to 8 of 8
Thread: condenser water pumps
-
09-10-2014, 10:14 PM #1
condenser water pumps
hello guys,
1- i have a condenser water pump of 102 L/s how much is the size of the pump? which catalogue i can find the selection for the pump.
2- the flow rate for the condenser water pumps is it based on 3usgpm/ton?
Thanks,,
-
09-10-2014, 10:50 PM #2
Re: condenser water pumps
Try one of the major pump manufacturers.
Lots of variables involved, duty, pressure, voltage, power consumption.
One choice - Grundfos Pumps
http://uk.grundfos.com/grundfos-isol...ler-unit1.htmlBrian - Newton Abbot, Devon, UK
Retired March 2015
-
10-10-2014, 12:58 AM #3
Re: condenser water pumps
Hi mah_h
as per Brian UK , there is a lot involved with selection of water pumps. Engage the services of a pump supplier that can analyse your application., then supply the correct pump or pumps.
-
10-10-2014, 04:58 AM #4
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 674
- Blog Entries
- 1
- Rep Power
- 19
Re: condenser water pumps
when you are choosing pump you rate better be in the medial of rang pump can work.
In condenser pump you need circulation pump and meanly 1450 RPM.
your inlet size for piping should be one size bigger than outlet size.
-
10-10-2014, 08:54 AM #5
Re: condenser water pumps
1 US Gallon = 3.8 Litres
3 US Gal/m/Ton = 3.8x3/60 =0.19 l/s/ton
102l/s / 0.19 = 631Ton of refrigeration = 2221kW
You will need a big pump
-
12-10-2014, 06:42 PM #6
Re: condenser water pumps
Thanks Brian
-
12-10-2014, 06:43 PM #7
-
12-10-2014, 06:44 PM #8