Water Chiller Technical Specification and Cable/Breaker Sizing
Dear fellow ,I am confused by technical specs of chiller and installed cable and breaker rating.
Following technical specs are written in chiller docs.
Absorbed Power = 86 KW
Nominal operating current = 145 A
Max operating current = 244 A
Now which of above parameter should be used for cable and breaker sizing? .
It is worthy to mention that chiller is water cooled twin screw compression chiller.
I have found that contractor has used 70 mm2 cable and 400 A rating breaker.
Please share your expert views as I suspect that above sizing is not compatible with chiller rating.
-
23-08-2014, 07:26 PM #2
Re: Water Chiller Technical Specification and Cable/Breaker Sizing
look at lra - locked rotor ampage, your lenght of cable run, type of cable used, whether its in free air, will determine your cable size, the fuses are designed to protect the cable from melting
see the link
http://www.openelectrical.org/wiki/i...ng_Calculation
-
23-08-2014, 07:34 PM #3
-
23-08-2014, 08:27 PM #4
Re: Water Chiller Technical Specification and Cable/Breaker Sizing
whats the make/model number of the chiller?, theres no harm in oversizing the cable -apart from the additional cost
-
24-08-2014, 06:45 AM #5
-
24-08-2014, 11:00 AM #6
Re: Water Chiller Technical Specification and Cable/Breaker Sizing
ive checked the sales info and doesnt state any compressor reference to check lra
best to contact the sales office as if your going to be buying 1 then they should provide you with an installation manual prior to ordering
Contact
70o klm Athens - LamiaHalkidaPO 191 73 34 100 Greece
+30 2262085600
+30 2262085728
http://www.interklima.gr
-
24-08-2014, 11:58 AM #7
Re: Water Chiller Technical Specification and Cable/Breaker Sizing
Let I put in simple what I intended to ask. (For the time
being put all other things aside, plz )Theoretically which of following parameter is considered for breaker/cable sizing?
Absorbed Power = 86 KW
Nominal operating current = 145 A
Max operating current = 244 A
-
24-08-2014, 12:04 PM #8
-
24-08-2014, 12:45 PM #9
Re: Water Chiller Technical Specification and Cable/Breaker Sizing
Voltage: 400V
Load: 221.7kW / 400A
Length: 20m
Method of Installation: Clipped direct
Cable Size: 150mm˛
-
24-08-2014, 06:17 PM #10
Re: Water Chiller Technical Specification and Cable/Breaker Sizing
I need your kind attention to following thread also.
http://www.refrigeration-engineer.com/forums/showthread.php?43614-Types-of-Current-Terms-in-an-Induction-Motor&p=299956#post299956
-
24-08-2014, 09:27 PM #11
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Water Chiller Technical Specification and Cable/Breaker Sizing
Cable is sized according to start method of compressors, allowable voltage drop, cable length, placement, ambient conditions and many more factors influencing proper function of Chiller.
Therefore, it is job for electrical engineer to make calculation and other details for correct cable size choice and installation.
Breaker is sized according to chosen cable and type is chosen according to maximum starting current and duration of start condition.Last edited by nike123; 24-08-2014 at 09:34 PM.