    plate chiller refrigerant recovery
    Hi guys ,Have to recover charge out of a small plate water chiller (14kgs) to repair a leak.System has no receiver and nowhere to recover liquid directly .Water will be running through exchanger at about 20c.Just still a bit worried about freezing in plate .Can any of you guys that have done this regularly offer any advice.
    Re: plate chiller refrigerant recovery
    Why should the refrigerant recovery cause any problems?
    It is being removed from the system, not flowing around the system.
    manchester
    5,639
    your water is circulating-at 20 deg so no issues
    ireland
    54
    275
    Its a plate chiller , there will be liquid trapped in the plate boiling off .The question im kinda asking is if the water is running through the system is ok to just recover full out or will i have to recover down to the freezing point and stop and let the liquid boil off above freezing point.
    ireland
    54
    275
    Sorry install was typing as you posted ,last post should have come out under brians,
    manchester
    5,639
    youve got a constant heat load, so no issues- if you wanted can you isolate the plate (water side) and drain it if your really worried- or disconnect the compressor,power up the chiller and moniter the flow ,return water temps
    ireland
    54
    275
    id be more worried about draining it in case there is any still water trapped in it .Amazing ,ive been around a while but never came across a water chiller before . Are we ever finished learning in this job.
    3,364
    Quote Originally Posted by joe-ice View Post
    If it has not been said already, keep the 20 deg C water flowing at all times & no problems if possible.
    ireland
    54
    275
    This is what im looking for .The machine is a cooling system on a laser lathe . If i pull the charge quick when theres 20c water has anybody seen ice to form in the exchanger.
    3,364
    Only if you do not keep water circulating
    3,853
    Also be careful when charging the system back up, till its above 0c saturation pressure.