09-08-2014, 09:39 AM #1
Daikin a0 fault
Hi
has anyone ever came across this fault code on a water cooled vrv4 system with only two hydro boilers connected
-
09-08-2014, 10:24 AM #2
Re: Daikin a0 fault
This could be an error in the external protection device or activation of the external protection device or an improper field setting. It could depend where the flow switch has been connected.
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.
-
09-08-2014, 10:30 AM #3
Re: Daikin a0 fault
What would be classed as a external protection.the flow switch is connected through 3 and 4 on the condenser.
-
09-08-2014, 05:20 PM #4
Re: Daikin a0 fault
Maybe a fire alarm interlock or remote time-switch possibly. Possibly a high/low water temperature stat. Electrical interlock with external pump contactor maybe.
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.