    Part winding Starting
    For the PW starting method, we are normally run 1/2/3 first, then 7/8/9
    But can i reverse it by running 7/8/9 first and then 1/2/3 ??? what any problem ?
    Thanks pro.
    AVICO
    Oct 2012
    Russia
    42
    392
    Re: Part winding Starting
    How power on windings is distributed?
    50%/50% or 70%/30%
    My question would be, why do you want to change it?
    Feb 2011
    Hanoi
    Quote Originally Posted by RusBuka View Post
    50%/50% or 70%/30%
    Hi, RusBuka. Power rate 70/30%
    Hi Brian_UK. Because sometime after overhauling, stator winding lead terminal mark is missing, so can not reg what (1/2/3 )or (7/8/9). So confusing
    Republic of south africa
    49
    184
    Assuming that your motor terminals are not swoped around after the overhaul you have to run the winding giving you 30%power output first then 70% 2nd. that is 123 first then 789 second
    Sep 2009
    Iran
    66
    674
    1
    both of them is same PW 1 and PW2 winding in screw compressors ( betzer )and time between them is about 0.5 second
    what is your compressor type?
    495
    Hi if your not sure which half of winding is bigger,get a multimeter and take ohms reading the bigger half will have lower ohms reading and smaller half of winding will have higher ohms readings .So always bigger half of winding should start first ,because other wise if smaller half starts first it wont have the power to turn and it will eventually burn out.
    Feb 2011
    Hanoi
    Quote Originally Posted by PRESS View Post
    Thank you
    But Do you agree with @GHAZ, wrote:
    Quote Originally Posted by GHAZ View Post
    Yes, that is 50/50 if PW1=PW2. my compressor is Frascold Italia, Screw type, 100Hp
    Thank you.