    Re: Walk in cooler issue, I am lost !

    Is this a TX, or capillary tube feed?
    Going to need the room and ambient temperatures for that day you wrote down your observations.

    The condenser fan motor failure might seem to be the original and only fault but the follow on effects from a dead condenser fan motor tend to bite you on the ass if you don't take the time to observe the kit's performance after repairs.
    Just sayin.....
    Last edited by mikeref; 26-06-2014 at 08:43 AM. Reason: Spacing my lines and topping up my glass of Morgan's.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Walk in cooler issue, I am lost !

    Paul Z on post # 10 has a valid point questioning op's pressure and temperatures.