Dynamic air conditioning E 5 error .
I have same error with 2 split sistems from Dynamic . Running fine half an hour and after that e5 error appears and the sistem stop . Starting again and running fine again . I did a check on the sensors but are fine . I don`t have any documentation on this split . I belive is maybe a problem with the indoor fan but i am not shure . Please if anyoane had the same problem tell me what should i check ? I must say i have different sistems same error ..12 k 18 kBtu .
-
15-06-2014, 11:23 AM #2
Re: Dynamic air conditioning E 5 error .
http://www.mediafire.com/view/m4oua3...ice_Manual.PDF
see if this shinco manual is similar- a lot of chinese stuff gets rebadged
E5 driver error- inverter circuit?
-
15-06-2014, 02:28 PM #3
Re: Dynamic air conditioning E 5 error .
No is an On-Off split sistem .
-
15-06-2014, 07:18 PM #4
Re: Dynamic air conditioning E 5 error .
If you provide photos of the units (better of the outdoors) I might be able to recognize the factory and give you a list of error codes.
E5 in most of the units is lack of communication between the outdoor and the indoor. Most probably indoor PCB problem.
-
15-06-2014, 09:50 PM #5
Re: Dynamic air conditioning E 5 error .
2014-06-11 19.45.34.jpg It`s a simple on-off sistem no comunication between Indoor and outdoor .
-
16-06-2014, 07:05 PM #6
Re: Dynamic air conditioning E 5 error .
Correct, it is not exactly communication, it is a "dry contact" being sent from the IDU to ODU.
If it doesn't work, then you might get the error.
However this label is not familiar to me at all... Unfortunately I can't help you with this unit.
-
16-06-2014, 08:01 PM #7
Re: Dynamic air conditioning E 5 error .
if all the sensors are giving the same resistance - indoor and outdoor, then check if your getting a signal to the outdoor- any condensate pumps with external fault contact, or some have a limit switch on the louvre motor- if they dont open fully then the unit just wont do anything
-
16-06-2014, 11:50 PM #8
Re: Dynamic air conditioning E 5 error .
No pump contact no floating switch . I just removed the electronic board and put a universal control board at 40 euro .....everything is ok now . **** China .