    Flush AC pipes



    Hi can any one tell me the best way to flush AC pipes out we have blown out with nitrogen but there is still lots of moisture in the pipes I know you can buy a chemical which you can flush out, the pipe work is in the ground and is 20 m runs



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Flush AC pipes

    Well if it is only moisture you are concerned about then the cheapest way of getting it out would be several successive deep vacuums broken by OFN...

    Cleaning agents is more for when the systems has suffered a burnout or brazing without OFN.


  3. #3
    northernbeach's Avatar
    northernbeach Guest

    Re: Flush AC pipes

    Dont challenge cleanse the lines with the utilization of an air compressor, you'll have different kinds of dampness in the framework.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Flush AC pipes

    Quote Originally Posted by northernbeach View Post
    Dont challenge cleanse the lines with the utilization of an air compressor, you'll have different kinds of dampness in the framework.
    Sorry don't understand this at all, can you please repost?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Flush AC pipes

    Ah, Brian,

    Translated to the queen's English, I believe it means:
    "Do not use an air-compessor to blow crap out of refrigerant lines as the result will be that you introduce more impurities to the system than you will remove from it"


  6. #6
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Flush AC pipes

    Compressed air via a good twin column dessicant dryer that`s had the dessicant recently changed, fitted with good quality line filters will get a PDP of -60c with particulate size of 0.01 micron. then use vacumm and OFN to remove the air. The air could be left on for several days, the only cost being the power used Of course that setup will cost money. but if you doing it on a large system and you can get the equipment used, it could make sense.

  7. #7
    Join Date
    Apr 2014
    Location
    Australia
    Posts
    7
    Rep Power
    0

    Re: Flush AC pipes

    Hi,

    Using a rubber tipped blow gun with the nitrogen pressure regulator set between the 5,0 –7,0 bar, blow
    nitrogen through the system.This will help you to eliminate any moisture that may be left in the system after flushing.

    Hope helps you!

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Flush AC pipes

    Put a tap on other end of pipes, pressurise the pipes as you see fit, shut off nitrogen, (PPE, googles gloves ear defenders etc) Open tap and sh!t flies out, repeat as necessary.