    Dec 2008
    UNITED ARAB EMIRATES
    49
    carrier 30xa-oil
    Dear all
    i have a 3 nos of carrier chillers model# 30xa0502g refrigerant 134-A compressor screw type. i need to replaced the oil i have not same carrier oil, i have only 4 option of oil. suniso 3GS, suniso 4GS, SL100, Emkrate RL-100H
    Please suggest me which oil i can use .
    Thanks,
    Re: carrier 30xa-oil
    According to the Carrier manual you can use the following...
    11.1.3 - lubricant The 06T screw compressor is approved for use with the following lubricants: • Castrol Icematic SW220 (Carrier specification PP47-32) • Lubrizol Emkarate RL220H (Carrier specification PP47-13
    Get the manual from....
    http://eto.carrier.com/lit.asp
    Mar 2014
    S.OF.OMAN
    44
    Sw220 u can use
    Jun 2006
    South Coast
    278
    DO NOT USE ANY OF THE OILS YOU HAVE MENTIONED above.
    Only use Castrol SW220 as previously stated by Brian.
    Why do you want to change the oil ?
    More to the point are you a refrigeration engineer ? if not then get someone who is to work on this chiller preferably Carrier.
    Some of the oil you mentioned above is Mineral Oil and a refrigeration engineer would know you don't use it on a R134A machine which only use's a Polyester oil ( POE).
    Dec 2008
    49
    Thanks all
    I got sw220 oil and I will replace same