    Hi All
    Hoping you can advise or help.
    I have a Gree Split unit 9000btu, (hummer) Model GWHN09EANK1A1A/I
    It has been installed for quite a while as an additional cooling aid but we don,t
    really use it all that much, but this year was extremely hot and found that we
    relied on it quite a lot, this is when i discovered that the unit is not switching off
    at the desired temp. and runs continuous. The unit is out of warranty but still like
    new.Is it possible to wire the sensor incorrectly and if so how can i check it, I don,t
    really want to get the tech guys out yet as I am a pensioner and the rates are so high.
    Maybe you could also advise where i can obtain a wiring diagram for this unit.
    Looking forward to your reply and help
    Kind regards
    rozzerh
    5,667
    Re: Gree split unit not cutting out at temp.
    Check for power at the relay when you are at thermostat off condition.
    Sounds like the relay contacts are welded.
    manchester
    5,639
    ring desa!
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    at the desired temp. and runs continuous."
    Are you saying it doesn't reach desired temperature....or it runs too cold? Chances are it can't get to the set point in hot conditions.
    Feb 2014
    South Africa
    4
    Hi all
    Thanks for all your responses i do appreciate it.
    Frank.... I am not a air con expert and know very little about the workings so you will have to treat
    me as a real novice.... Is the Relay in the outdoor unit or in the Indoor unit and how do I test it?
    Install monkey..... What or who is DESA?
    Mikeref.....It does reach the desired temp and in fact probably lower than required, I tested yesterday
    and set the remote to 25degC and checked the room temp later and it was 23degC and at the
    intake side of the indoor unit it was 24.3degC. and the unit was still running.
    If i set the temp. to 20degC it cools to that temp and lower but still keeps running. Its as if the
    sensor is not reading it if thats possible, thats why i asked if it can be connected wrongly.
    This means I can not run the unit during the hot nights as it gets too cold and has to switched off
    and on manually throughout the night.
    Thanks one and all
    Regards rozzerh
    manchester
    5,639
    usually the indoor is powered and this supplies the outdoor unit- if so then the power relay is usually mounted on the indoor pcb
    if its power to outdoor and then the contactor/relay will be in the outdoor unit
    sometimes theres a wiring diagram on the outdoor unit somewhere
    if there was a sensor miswired then the unit would alarm, usually with flashing lights on the indoor
    jigga23's Avatar
    jigga23 Guest
    hi what is the area of the room and does the remote have a "fast cool" or "turbo" button maybe the function is on and that will cause it to run continues
    manchester
    5,639
    are the filters clean?
    Feb 2014
    South Africa
    4
    Hi all
    Once again thanks for your help
    Install monkey......Cable from the power supply runs from the inside plug point to the outside
    into a ducting and obviously back in at the top to the indoor unit, so i will have to get up and open up the cover to see which is fed first, I can also look for a diagram...The outdoor unit is about 3m up the wall so
    as soon as i can do it i will get back to you.......The filters are like new.& no flashing lights
    to indicate a wiring fault.
    jigga23.....The area of the room is 3.8m x 4.4m (16.72).....There is a turbo button but i checked
    and it is switched off.
    Regards rozzerh
    Feb 2014
    South Africa
    4
    Hi all
    Just an update to my problem as above.
    I managed to get the guys who installed the units to check them out
    and they found the sensors faulty, they said it was a pretty common
    problem with these units. They replaced them and all seems fine now.
    I asked for the old ones and don't know if there is a way to test them
    and apparently they come in a set of 2.
    Regards Rozzerh