    samsung floorstand split ac problem



    hi
    i installed a Samsung floor stand split unit
    its heat pump
    28000 btu
    and model is AP30N1A
    the unit is working perfectly
    as i use it in cooling mode
    its normally that after the desired temp is reached
    the outdoor unit is turnoff and indoor unit keep running
    but
    the problem here
    when the desired temp reached
    the outdoor unit turn off and indoor unit shutdown then its turn on after 2 second
    and when the room temp equal the set temp
    the outdoor unit run
    so why the indoor unit turn off then turn on
    what is the problem
    this happen every time
    and the unit cools very excellent



  2. #2
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    up
    up
    up

  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem


  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: samsung floorstand split ac problem

    Link document fails
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    it worked for me the link- i clicked to open as opposed to download- its for a floor standing unit- but not the normal type- the big tall narrow ones - cant find anything on google or other branded search engines

  6. #6
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by Brian_UK View Post
    Link document fails
    try this
    http://dc581.2shared.com/download/PA...20148-b8b32113

  7. #7
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by install monkey View Post
    it worked for me the link- i clicked to open as opposed to download- its for a floor standing unit- but not the normal type- the big tall narrow ones - cant find anything on google or other branded search engines
    you read the manual or not

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: samsung floorstand split ac problem

    OK got the manual but it doesn't have any useful information in it to explain the inner workings of the machine
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by Brian_UK View Post
    OK got the manual but it doesn't have any useful information in it to explain the inner workings of the machine
    ok
    some people told me that in cooling mode the indoor unit (fan and led ) will turn off when desired temperature is reached
    due to
    frosting in indoor
    energy saving
    anti air draft function
    so how to ensure that i dont have problem
    Last edited by kefah; 19-06-2013 at 09:44 PM.

  10. #10
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: samsung floorstand split ac problem

    Kefah.

    Why have you PM'ed me twice about this? Have you mistaken me for somebody else?

    Cheers

    eggs

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: samsung floorstand split ac problem

    Eggs,he normally PM's me every time he starts a thread for some reason, he must think that you are the man with the answers.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: samsung floorstand split ac problem

    Or he figured out that we are closet Liverpool fans...



  13. #13
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: samsung floorstand split ac problem

    Quote Originally Posted by Brian_UK View Post
    Eggs,he normally PM's me every time he starts a thread for some reason, he must think that you are the man with the answers.
    I'm a ducter with a vac pump and ideas above my station

  14. #14
    Join Date
    Jun 2013
    Location
    China
    Posts
    1
    Rep Power
    0

    Re: samsung floorstand split ac problem

    Please check the air conditioner emergency switch and compressor relay contral is ok.

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    does tri county do service calls to iraq????
    Quote Originally Posted by Borisward View Post
    I think you need to consult it with professional ac repair provider who can provide its better solution and check it for you that what's the problem there in your AC.http://www.tri-countyac.com/ac-repair-tamarac
    Last edited by install monkey; 22-06-2013 at 10:53 AM.

  16. #16
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by eggs View Post
    Kefah.

    Why have you PM'ed me twice about this? Have you mistaken me for somebody else?

    Cheers

    eggs
    sorry
    that happened mistakenly

  17. #17
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by Brian_UK View Post
    Eggs,he normally PM's me every time he starts a thread for some reason, he must think that you are the man with the answers.
    i pm you and others
    because i know you have the most correct answer
    and i appreciate that from you
    sorry for disturbing

  18. #18
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by Borisward View Post
    I think you need to consult it with professional ac repair provider who can provide its better solution and check it for you that what's the problem there in your AC.http://www.tri-countyac.com/ac-repair-tamarac
    thanx for nothing

  19. #19
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: samsung floorstand split ac problem

    sounds to me like its working ok...bit strange but working ok, after all if you haven't got a problem like freezing indoor unit/excessive condensation then why ask

  20. #20
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by jdunc2301 View Post
    sounds to me like its working ok...bit strange but working ok, after all if you haven't got a problem like freezing indoor unit/excessive condensation then why ask
    the unit works perfectly
    but i wondered why sometimes the indoor unit turn off for seconds when set point temperature reached
    instead of keep running

  21. #21
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    normally in auto the indoor fan will go into low speed until it deviates off setpoint- but power/operation led will stay lit- check resistance of the return air sensor and coil sensor too ensure theyre both reading similar resistances with the unit off for 10 mins.

  22. #22
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by install monkey View Post
    normally in auto the indoor fan will go into low speed until it deviates off setpoint- but power/operation led will stay lit- check resistance of the return air sensor and coil sensor too ensure theyre both reading similar resistances with the unit off for 10 mins.
    both indoor fan
    power/operation led turn off for second
    then turn on again

  23. #23
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    this week
    i made some check on it
    when the unit was run and temp of room was 22 c
    and set point was 20 c
    the unit was cooling perfectly for 2 hours
    i raised from the remote control the set-point to 24 c
    so the outdoor unit stopped working
    and the indoor kept run normal without shutting down
    and when room temp increased to 24 c (setpoint)
    the outdoor run again
    so no problem
    yesterday
    the setpoint was 18 C
    and room temp was 28 c
    the unit worked perfectly in cooling
    when setpoint reached
    outdoor unit shutted off
    then indoor turned off (LED screen and indoor fan) shut off also
    and after about 20 minutes its auto run again
    then after 3 minutes the outdoor unit worked also
    during the shut off period
    the voltage was 215 v
    current was 0,18 ampere
    some expert said that the shut off happen may be due to defrost of indoor unit coil
    but the question here
    if it was defrost indoor
    by using electric heater on evaporater
    why the current was 0.18 amp
    and if the defrosting was without heater (by normal defrost which mean leaving the unit melting the ice by its self)
    is that mean it may take 20 minutes to finish
    please helllllllllllp

  24. #24
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23
    The operation seems normal, 3 min delay on compressor start... Use a calibrated temp sensor and when the unit reaches its set point and shuts the indoor fan off measure the temperature when the indoor fan comes back on to see if it turning on with a temperature rise.... I think you should let this unit be now...as it doesn't sound like its causing problems..just your curiosity

  25. #25
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    might be a voltage drop- ask your boss to increase the output frequency- nowt like a bit of smoke in the air! haha

  26. #26
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by jdunc2301 View Post
    The operation seems normal, 3 min delay on compressor start... Use a calibrated temp sensor and when the unit reaches its set point and shuts the indoor fan off measure the temperature when the indoor fan comes back on to see if it turning on with a temperature rise.... I think you should let this unit be now...as it doesn't sound like its causing problems..just your curiosity
    ok
    why the indoor unit shutted off for 20 minutes
    i think its long time

  27. #27
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by install monkey View Post
    might be a voltage drop- ask your boss to increase the output frequency- nowt like a bit of smoke in the air! haha
    voltage is 200 v

  28. #28
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    gotta be going out on freeze protection- when it runs for 2 hrs ok no where near its setpoint, then when it cuts out on stat indoor cuts in and out- pull the evap coil sensor off the coil to see how it works
    cannot find any service manuals for this- is the mains power to outdoor or power to indoor?
    Last edited by install monkey; 30-06-2013 at 10:23 AM.

  29. #29
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by install monkey View Post
    gotta be going out on freeze protection- when it runs for 2 hrs ok no where near its setpoint, then when it cuts out on stat indoor cuts in and out-
    did the freeze protection will take about half hour
    is this normal

    pull the evap coil sensor off the coil to see how it works
    i will check

    is the mains power to outdoor or power to indoor?
    main power is to outdoor unit
    and there is only 1 PCB in the unit in the indoor unit

  30. #30
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23
    Have you checked what temp this unit is turning off and on at and the set point?

  31. #31
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23
    I would recommend that you set up a tent... Remove the covers and run in cooling and physically watch the unit and monitor the temperature of the coil on and off temps including the actual coil temp and then report back to us once you can verify what the unit is doing... Reaching sp etc or not... Cause it's either a defrost or a weird way of running the unit... And I would punt at either as we can't find manuals for the unit..... In the meantime please take note of this chart.......for the future

    image-160685374.jpg

  32. #32
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    how long is the piperun,any additional charge added,what are the running pressures, current draw at the condenser

  33. #33
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by jdunc2301 View Post
    Have you checked what temp this unit is turning off and on at and the set point?
    the unit turn off at set point temperature
    and after it turn on ( after seconds minutes)
    when the desired temp reached outdoor unit run again

  34. #34
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by jdunc2301 View Post
    I would recommend that you set up a tent... Remove the covers and run in cooling and physically watch the unit and monitor the temperature of the coil on and off temps including the actual coil temp and then report back to us once you can verify what the unit is doing... Reaching sp etc or not... Cause it's either a defrost or a weird way of running the unit
    the unit works perfectly
    until it reach the set point
    and if the doors was open
    and set point didn't reach up
    it run for hours with out problem

  35. #35
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by install monkey View Post
    how long is the piperun,any additional charge added,what are the running pressures, current draw at the condenser
    the pipe long 5 meter as from manufacturer
    and suction pressure 68 psi
    current 13 amp

  36. #36
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    i contacted samsung service
    and they told me this weird thing
    they said that cause of the problem is
    bad power supply ( transformer ) of the PCB
    and all the similar unit have the same issue
    so im wondering if the transformer is bad
    why the unit keep run for hours without problem ????????????????
    if setpoint not reached
    and if the transformer is bad
    why this issue happen only when set point reached ??????????

  37. #37
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    if samsung have answered your question with a diagnosis of the problem, then who are we to question the wrath of the manufacturer- get the replacement board and try it

  38. #38
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by install monkey View Post
    if samsung have answered your question with a diagnosis of the problem, then who are we to question the wrath of the manufacturer-
    they are liar
    because if it was bad transformer
    then the unit will not run for 6 hours without problem


    get the replacement board and try it
    they asked for 35 dollar

  39. #39
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: samsung floorstand split ac problem

    what if there's a poor joint on the pcb or if a pcb component is getting hot- ask e if the 35 dollar is refundable if it still has the same problem when u swap it!
    they have highlighted an issue with the pcb, some muppets on technical dept can spout crap regarding the cause and reason, its not unusual for faulty pcbs, if there is 2 of these units you could swap pcbs to test this theory, otherwise your going to be checking,eliminating all other avenues to come to the same conclusion of indoor pcb.
    Quote Originally Posted by kefah View Post
    they are liar
    because if it was bad transformer
    then the unit will not run for 6 hours without problem



    they asked for 35 dollar

  40. #40
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    Quote Originally Posted by install monkey View Post
    what if there's a poor joint on the pcb or if a pcb component is getting hot- ask e if the 35 dollar is refundable if it still has the same problem when u swap it!
    they have highlighted an issue with the pcb, some muppets on technical dept can spout crap regarding the cause and reason, its not unusual for faulty pcbs, if there is 2 of these units you could swap pcbs to test this theory, otherwise your going to be checking,eliminating all other avenues to come to the same conclusion of indoor pcb.
    thank u
    the weird think
    is when i asked them if i didnt replaced the transformer
    what will happen
    did it will burn or damage the PCB
    they answered there is no problem in keeping the same transformer for 5 years
    !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

  41. #41
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    today
    i checked another air conditioner split from same model
    with same issue of mine
    so is that could be normal

  42. #42
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    finally i took my PCB to Samsung service center
    here what they did
    the removed the transformer and some diode
    and soldered an external transformer
    then i installed the PCB
    the unit worked perfectly
    and when the set point reached
    only outdoor unit turn off while indoor unit kept on working
    the problem now
    the LCD screen is not working normally
    its look like its not receives voltage normally
    i opened the panel to discover that they replaced the old transformer with one hiher wattage but lower voltage
    the PCB is 12 v
    and they used 10.8 v
    so i removed their transformer
    and i bought anew one 12 volt
    now every thing is good
    thank u all for helping me

  43. #43
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: samsung floorstand split ac problem

    Well done fella, you got there in the end. Thanks for the update.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  44. #44
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    624
    Rep Power
    17

    Re: samsung floorstand split ac problem

    thank u Brian