    Green Flashing light- fault on Airwell



    Hey lads, I've a problem with an Airwell Cassette. M: KXL 36NT R410A AW. It heats fine but when I put it into cooling mode the green light on the fascia starts flashing and I have no cooling from the system. Is there any way to get a fault code or anything off the system or is it a matter of literally checking everything? My first stop will be the 4 way valve anyway. It's on a RCW2 controller if that helps.

    Thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Green Flashing light- fault on Airwell

    check hi limit float switch isnt stuck in the fault position- can disable cooling

  3. #3
    Join Date
    Mar 2011
    Location
    Dublin
    Age
    37
    Posts
    55
    Rep Power
    14

    Re: Green Flashing light- fault on Airwell

    Quote Originally Posted by install monkey View Post
    check hi limit float switch isnt stuck in the fault position- can disable cooling
    I'll check it out thanks. I did pour 2 litres into the port at the back to test the pump, which worked.