    Hi All,
    Been working on a site which has 4 ammonia glycol chillers.
    The was not an emergency shower on the site for these chillers.
    Each holds around 125kg of charge but I was told that an emergency shower is not required for the site because of the low charge of the plants but it just seems silly that an ammonia plant regardless of charge does not have an emergency shower, or eyewash station?
    Can anyone give me some information or more specifically the regulations so I can read for myself?
    thanks
    scott
  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    60
    Posts
    1,528
    Rep Power
    37
    Re: Ammonia Drench Showers + Regs
    EN 378,2-2008
    Section 5.17.2.2
    Systems containing more than 1000kg of R717 shall be provided
    with a shower providing 50l/m at 25 degs to 30 degc outside the
    emergency exit.
    Rob
  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,702
    Rep Power
    47
    You beat me to it Rob!
    However in part 3 it does say that an eyewash station is required irrespective of system/s charge with Ammonia and other caustic skin or eye irritant refrigerants!
    Grizzly
  4. #4
    Join Date
    Mar 2012
    Location
    United Kingdom
    Posts
    17
    Rep Power
    0
    Thanks for your response guys.
    With regard to an eyewash station, are the little saline tubes classed as eyewash station? They seem very inadequate for the intended purpose.
  5. #5
    Join Date
    Mar 2012
    Location
    United Kingdom
    Posts
    17
    Rep Power
    0
    Do either of you guys have a copy of these sections of the regs for me to have a look at?