    York YCAJ77XT9 chiller



    We have a York YCAJ77XT9 chiller to decommission.
    Unfortunately, we have not had the opportunity to visit the site and wondered if anyone has any details as to the quantity of refrigerant that ought to be in this chiller?
    We believe that it is about 530kW, not that that is much help.
    Many thanks.


    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: York YCAJ77XT9 chiller

    mileninium gsi
    if its heat recovery 76kg circuit 1 and 52kg circuit 2 if standard then 52kg per circuit r407c
    23ltr of oil total
    507kw
    5040kg - for scrap purposes- buy some 9 inch grinding discs- if you disect it correctly you can get about 2k for it
    Last edited by install monkey; 03-02-2014 at 09:17 PM.

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    563
    Rep Power
    24

    Re: York YCAJ77XT9 chiller

    Thanks I.M. and Grizzly for the info.