    Jan 2014
    United Kingdom
    54
    Capacity Slide problem
    Unable to start the compressor due to the capacity slide value being at 19%, Is there anyway of reducing this so the compressor can be started?
    Jun 2011
    Australia
    44
    336
    Re: Capacity Slide problem
    Can you change the parameter value for minimum start position?
    I often use a instrument signal generator as work around.
    Jan 2014
    United Kingdom
    54
    iF i get the capacity slide value to read 0% , the compressor will start with a loading of 19% will this be ok
    Jun 2011
    Australia
    44
    336
    I've seen compressors start at 100%, the lights go pretty dim for a while..
    Jan 2014
    United Kingdom
    54
    Right thats what i was worried about I can fabricate a 0% but just uncertain of starting the compressor under load
    3,363
    Type of compressor & control system would be helpful to diagnose problem.
    Each brand has its own characteristics etc.
    There must be a reason for it to lose calibration, or a least check possibilities.
    Once you reset 0%, you then have to re-calibrate 100% to get most out of your machine.
    Jan 2014
    United Kingdom
    54
    There are two compressors , a H.P Compressor and Booster compressor with unisab controllers and a trend IQ151+ CONTROLLER. NH3 system chilling a tunnel at -45
    70
    4,700
    47
    Quote Originally Posted by Markridgway View Post
    As ranger implies it depends what screws you have.
    I have carefully bled the slide return oil line before now.
    To break the hydraulic lock that can sometimes occur following a unscheduled shutdown.
    It can get a bit smelly and synthetic oils are messy.
    But it works as the slide should then return to its stop under the spring alone.
    Careful mind!
    Grizzly.