Results 1 to 12 of 12
  1. #1
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Close Control but no heat load



    I'm looking at quoting a small room (27m2, 3m ceiling) which requires conditions of 21-24degC and 45-55% RH.

    The only heat loads are 2/3 personnel, pc's (the usual office kit) and some solar gain in the summer. Throughout the winter they will require heating and humidification.
    (I've worked out the cooling load at 3.3kw/heating load 3.4kw)

    Can anyone recommend a close control system for this application? (cool/heat/dehum+reheat/humidify) Been looking into Airedale but just wanted to see if there's anything else.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Close Control but no heat load

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2008
    Location
    england
    Age
    40
    Posts
    113
    Rep Power
    18

    Re: Close Control but no heat load

    Quote Originally Posted by Slim R410a View Post
    I'm looking at quoting a small room (27m2, 3m ceiling) which requires conditions of 21-24degC and 45-55% RH.

    The only heat loads are 2/3 personnel, pc's (the usual office kit) and some solar gain in the summer. Throughout the winter they will require heating and humidification.
    (I've worked out the cooling load at 3.3kw/heating load 3.4kw)

    Can anyone recommend a close control system for this application? (cool/heat/dehum+reheat/humidify) Been looking into Airedale but just wanted to see if there's anything else.
    Sounds like a Daikin Ururu Sahara split (Has a Humidty control)will do this pretty sure Airedale do a 5kw as the smallest but i could be wrong

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Close Control but no heat load

    daikin ururu sarara is a very feeble excuse for close control- the controller will only let you set a hi med low humidity range- and it relies on outdoor air to provide the moisture- good for domestic use but you need to go to denco,airedale,eaton williams or other similar brands
    Quote Originally Posted by leegally1983 View Post
    Sounds like a Daikin Ururu Sahara split (Has a Humidty control)will do this pretty sure Airedale do a 5kw as the smallest but i could be wrong

  5. #5
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Close Control but no heat load

    Quote Originally Posted by install monkey View Post
    daikin ururu sarara is a very feeble excuse for close control- the controller will only let you set a hi med low humidity range- and it relies on outdoor air to provide the moisture- good for domestic use but you need to go to denco,airedale,eaton williams or other similar brands
    Exactly, I've gone for a 6kw Airedale Easicool.

  6. #6
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: Close Control but no heat load

    i would recommend the GEA Heat Exchanger Multi-Denco system.......but then....I would!

  7. #7
    Join Date
    Apr 2011
    Location
    England
    Age
    35
    Posts
    41
    Rep Power
    0

    Re: Close Control but no heat load

    are the airedale units electric heating only or do they make heat pumps?

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Close Control but no heat load

    airedale now do carbon heating- with real flame effect- check the office in leeds! scorchio! haha

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Close Control but no heat load


  10. #10
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: Close Control but no heat load

    Quote Originally Posted by install monkey View Post
    airedale now do carbon heating- with real flame effect- check the office in leeds! scorchio! haha
    Well, at Denco, despite the increase in sales, we didn't rejoice at the Airedale factory burning down. Those are people jobs and lives at stake and fire destroys business' and there but for the grace of God go I

  11. #11
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    16

    Re: Close Control but no heat load

    Let us look at HiRef but on NRG series
    http://www.hiref.it/images/stories/B...G_en_ru_de.pdf
    Last edited by bigor_2; 20-01-2014 at 08:12 AM.

  12. #12
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: Close Control but no heat load

    Stulz do a 5kW system.

Posting Permissions