    Re: R404a water cooled condensing unit with 8oC cooling water

    Your condenser water leaving temperature must be above 30°C, or you will not have enough pressure diferential required for proper function of TXV. Therefore, you will need to mix condenser leaving water with some portion of water coming in bypass with condenser in order to get water leaving temperature of less than 15 or whatever you prefer.