Results 1 to 18 of 18
22-08-2013, 10:08 AM #1
Choosing the evaporator and condensator
I am currently in a project in which I have to design an AC unit, and since I am pretty new to this whole world (I am in my practical placement as an engineer), I have some questions regarding the choosing of components.
When choosing the evaporater and the condenser, which elements influence the choice, as I understand it you have to choose it from the needed capacity, but almost everyone i look at is overdimensioned by a lot?
How do you calculate what the necessary heating exchange area should be?
Lastly, can you recommend any good suppliers of evap. and cond. coils?
Kind regards
Michell
22-08-2013, 12:01 PM #2
Re: Choosing the evaporator and condensator
The most important thing is knowing the product you are cooling.
Water, milk, beer, beef, broccoli, Brussel sprouts, people, air
all require different amounts of cooling so you need to know.
Your talking of an AC system so you are dealing with a room
full of people and for the most part AC deals in comfort cooling.
Comfort cooling is the required temperature for a certain period
in the year, so you can size the system to deliver comfort cooling
for, say 300 days in a year, that means for 65 days when the temps
get too cold or too hot the system starts to struggle.
It depends on cost and
How many people?
Where is the room?
How many light fittings, PC's, workstations and other such things?
Windows, how big and facing what direction?
When you know all these things they all add up to a heat load and
that is how you start to calculate your requirements.
Doing it on the cheap means you could put a system in a few Kw smaller
than needed and it would work for the most part except when the weather
gets too hot / cold or you could go the other way and put a system in that
is a few Kw over sized and that would work 365 days a year but cost a lot
more the install.
It comes down to cost........
Rob
22-08-2013, 12:15 PM #3
Actually it is electronics cooling, i forgot to mention that earlier -.-
I have gotten the cooling capacity from the customer and they calculated it to 300W.
But I am struggling on how to decide the appropriate evaporator and condenser size.
Ragards
Michell
22-08-2013, 01:32 PM #4
300w is nothing compared to even a small AC unit.
Are you dealing with processor cooling because that is a whole
different kettle of fish?
Electronics in a room is more closely controlled and tends
to use close control systems, not just AC systems.
All rooms have a heat load and then find the heat loads
of the electronics and then allow for them. Electrical
equipment have wattage or Kw outputs on them so by using
those values you can work out the total.
There are quite a few free software packages online or
you can use generic rules of thumb (all manufactures have them)
and calculate from there.
But be aware that when cooling electronics, redundancy tends
to be built in.
So for example if 15Kw of cooling was required instead of putting
1 X 15 Kw system or 2 X 7.5 Kw systems in you might consider
putting 3 x 7.5 Kw so if one fails you have a bit of redundancy.
Rob
.Last edited by Rob White; 22-08-2013 at 01:35 PM.
22-08-2013, 01:40 PM #5
With the heat loads from the electronics the cooling capacity should be 300W it is inside a cabinet so it is a small confined space.
The only thing I was actually wondering about is what factors are used when you are deciding the actual component :-)
Michell
22-08-2013, 01:46 PM #6
And how to calculated the necessary heat exchange area of the evap. cond. :-)
regards
Michell
22-08-2013, 03:53 PM #7
Hi, WootAC
Welcome to RE forums ...
Not sure, but I believe if you check this forum maybe you'll find what you need .... or at least someone who can help you with equipment you need ...
http://www.refrigeration-engineer.co...U-Overclockers
here you can find such a small cooling unit ... I hope
Best regards, Josip
22-08-2013, 04:04 PM #8
Yeh there has been a lot of discussion re cooling
PC boards and it is done in quite ingenious ways
Rob
22-08-2013, 07:02 PM #9
Cooling boxes are commonly available for electronic enclosures. I've worked on several machining centers that use them to provide cooling without admitting contaminated external air to the cabinet. Refrigeration capacities range from a few hundred watts to several kW.
We have two of these cooling units on our main PLC cabinets. Basically, they are just glorified window shakers with absurd price tags. Cheaper than building from parts though.
22-08-2013, 09:06 PM #10
rittal make small coolers
23-08-2013, 08:06 AM #11
I am actually more interested in how you buildt a unit from scratch, as I wrote before I am an engineering trainee and are very interesed in how the whole system works and how to decide on which components are right for the given job. I must admit that I am still unsure on some of the basics ex. what happens physical and theoretical with the fluid during startup, and how do the system responds if you use a capillary tube and run the sytem below the disigned ambient temperature.
An example could be :
ambient temperature 55 celcius and target temperature in the enclosure is 25 celcius.
A capillary tube is used to regulate the pressure
I know the ambient temperature is pretty high but this kind of device may need to be deployed in desert/jungle enviroment so that is the reason why it is this high.
How does the fluid react (physical and theoretical) if the "start supply" temperature on the evaporator side is equal to the ambient temperature?
And how will the system then respond if it is used in, lets say 30 celcius ambient suddenly?
Michell
24-08-2013, 10:18 AM #12
1. Known : Target cooling capacity : Q',e.
2. Add in safety factor => Lock design cooling capacity : Q',evap.
3. Determine
3.1 Evaporator end
3.1.1 Cooled part - operating temp : Tp,m
3.1.2 Allowable DT,e for cooled part - say DT,e=Tp,m - Te,sat (nominal point)
3.1.3 Te,sat = refrigerant saturation temp in evaporator - determined
3.2 Condenser end
3.2.1 Sink temperature (where the heat goes to) - Th,m
3.2.2 Allowable DT,c for condenser - say DT,c=Tc,sat-Th,m
3.2.3 Tc,sat = refrigerant saturation temp in condenser - determined
3.3 Compressor
3.3.1 Assume an operating efficiency (other approaches also work).
3.3.2 Plug into Coolpack - run
3.4 Determine
3.4.1 Q',cond = condenser heat load
3.4.2 W',comp = compressor power input
3.4.3 m',ref = refrigerant mass flow-rate around circuit
Known - to this point: Q'evap & Q'cond
Head to Coolit software site, to see if their coil programs will assist for the condenser end of your design - if air-cooled.
The evaporator part will, in all likelihood, be a specifically-designed component. Here you'll need to understand a little more about two-phase flows & forced evaporation. A fair bit of reading up for you here. A useful book to look for is :
Heat Transfer and Fluid Flow in Minichannels and Microchannels - Kandlikar S.G, et al - Elsevier
Iterate a few times, with incremental changes in one variable at a time. Refine solution.Last edited by desA; 24-08-2013 at 10:25 AM.
25-08-2013, 02:31 PM #13
Use a Peltier element for such a small capacity.
26-08-2013, 07:00 AM #14
Peter:
Have COP's improved much over the years?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
26-08-2013, 08:19 AM #15
Thanks for the answer desA, we needed some sort of plan on how to begin the project!
Peter_1
We have already looked at Peltier devices, but the efficiency is way too low for the customer, so we quickly turned away from that again.
26-08-2013, 02:03 PM #16
Absolute pleasure, WootAC. You'll learn a great deal along the development pathway.
What compressor type have you in mind?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
26-08-2013, 02:24 PM #17
I hope so, it is pretty complex to understand every aspect of the AC unit so we have broken it down into the different components and are now on our way to designing one for our self.
We are currently looking at micro rotary compressors (aspen, Purswave etc.), because we have a limit regarding the dimensions of the whole unit. But we have also looked at the slightly larger compressors from SECOP and Masterflux :-)
Michell
26-08-2013, 03:05 PM #18
You are on the right track. Let us know how you get on.
Remember, at all times : The evap/compressor/cond/restricter/piping/fans/pumps are all part of a system. One small change in one component will change the system equilibrium point.Last edited by desA; 26-08-2013 at 03:08 PM.