    Toshiba evaporating to low



    I have a Toshiba ducted unit 12 kW giving out an air temperature of 6 C causing condensation.
    Could exp valve be faulty? I have tried everything else without stripping down the outdoor, gas charge ok weighed out and recharged, changing over to heat no problem. No faults on controller but when I put into test mode got E 04 communication error. any ideas?



  2. #2
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Toshiba evaporating to low

    What's your air on temp? Have you good airflow across the coil? Any supply/ return air grills shut? Any restrictions on the ductwork?

  3. #3
    Join Date
    Aug 2001
    Location
    ireland
    Posts
    34
    Rep Power
    0

    Re: Toshiba evaporating to low

    Air on temp 24 feed by 4 ducted return grills, all fully open no blockages.??Fan speeds adjusting ok

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Toshiba evaporating to low

    air flow too low -is it on high static setting?

  5. #5
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    22

    Re: Toshiba evaporating to low

    Hi Techni,
    First off what model indoor \ outdoor do you have?
    I'd put my money on poor air flow too. I frequently come across ducted indoor with incorrect ducts installed - especially with ducted returns too.
    You don't say what fan speed you are using to do the tests on. Higher is better.
    You need to check the air volume and compare to the specs Tosh provide.
    Also think about under sizing - if the kit runs constantly either it's not performing or is undersized - either of which could lead to grilles getting too cold and dripping moisture.
    Some Tosh models (R22 & R407c) came with a 'jack up' loom to boost the air volume too.
    An unlikely one (given it's summer) but could your system be over condensing?

    Let us know what you find.

    Cheers

    Loops

    PS I used to work for Tosh tech dept