    R22 Mitsi Pury ~ Anyone converted to R417a
    Model is PURY250YMF 30kW with 5 cassettes.
    Best option is to replace the kit and keep the pipework, etc, but there is this option that customer wants info on. I was wondering if any engineers on RE had experiences in converting these condensers/systems to R417a, and it all worked out fine, or any problems etc.
  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45
    Re: R22 Mitsi Pury ~ Anyone converted to R417a
    hitatchi dont recommend it on their vrf's
  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36
    Last quote I had for a drop in (R437A and some other one, not 417A though) both came out over 4.5 times the price of the normal refrigerants. Might be something to bear in mind if you ever suffer any refrigerant loss and no doubt the drop in would have gone up in price by then.
    Mind you, perhaps 410A be getting phased out then as well, hee hee.
    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.
  4. #4
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    24
    R417A is recommended for applications under 15kw only.Would be better to sell them a new system.
  5. #5
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21
    Quote Originally Posted by Gibbo View Post
    Yes, that was the area I was interested in. Have had a few 5kW spilts converted that went okay in the past, but 28kW VRF is a bit more than 15kW. Hence the question for anyone else having done it.