    Sep 2005
    India
    30
    Condensing temp in refrigeration
    I am confused with the term, "Condensing temp".
    When we say condensing temp,
    1. Is it the temp of condensing medium (in case water cooled condensor, water temp) or
    2. the refrigerant gas leaving compressor has some condensing temp? if so, how to decide?
    Anup
    Oct 2003
    5,630
    Re: Condensing temp in refrigeration
    At the compressor discharge valve, you have the discharge temeprature.
    It is the hottest measurable point in a system (the discharge valve is the hottest point)
    It is in this point that we find all the collected heat of a system.
    In the condenser, we first have a desuperheating and then we come to the condensing temperature.
    This is the biggest part in the condensor where we have a saturated condition which means that there is a relation between temperature and pressure.
    This is also the pressure - the condensing pressure - you read on your manifold and the temperature you find on the dial of your manifold or on a sliding ruler is the condensing temperature.
    When liquid leaves the condensor in the last part, it will sometimes a little bit subcooled. You still have the same condensing pressure but you now have a lower liquid temperature then the condensing temperature.
    Clarified?
  1. Ultra low Temp Refrigeration
    By elmusasc in forum Industrial
    Last Post: 31-07-2011, 07:00 PM
  2. Ultra low temp refrigeration
    By Nuklhed in forum Refrigeration Books
    Last Post: 25-03-2006, 03:05 PM
  3. Condensing temp of refrigerant
    By anup in forum Fundamentals
    Last Post: 04-10-2005, 03:14 PM
  4. condensing temp rule of thumb
    By angryk in forum Fundamentals
    Last Post: 14-03-2003, 04:00 AM