    Panasonics CU-25R --What DCV at terminal of out door unit in normal operatioin ....



    refered to ..

    http://www.refrigeration-engineer.co...lp-me-any-body

    My panasonics inverter air-con CU-25R show H11 error like that.

    I've read the answer from that page and want to know more about the DCV. at terminal 2-3 on O/D unit at normal operation.

    Many Thanks.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonics CU-25R --What DCV at terminal of out door unit in normal operatioin .

    Is there any wiring error?
    Correct the indoor-outdoor units
    connection wires
    Check the indoor-outdoor units’ connection wires.
    Disconnect terminal 3 wire and measure Vdc between terminal
    2 & 3 from the outdoor unit.
    Is the Vdc fluctuate between 20-70Vdc?
    Replace outdoor PCB
    Reconnect terminal 3 wire and measure Vdc between terminal
    2 & 3 from the outdoor unit.
    Is the Vdc fluctuate between 20-50Vdc?
    Replace indoor unit PCB.


  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonics CU-25R --What DCV at terminal of out door unit in normal operatioin .

    check your wiring isnt crossed between indoor/outdoor
    check indoor fuse spur connections ok, and only switching 240v live and neutral- check wire 3 is thru crimped or terminal block- not switched or any external condensate pump hi pump alarm float isnt wired in

    if unit still shows h11
    then isolate outdoor unit, remove wire 3 (comms line)
    test 2-3 should give a pulsating dc voltage upto 50vdc
    if not check fuses,connection plugs on outdoor boards
    i had a 48-50vdc signal on 1 and appeared to be indoor pcb, after swapping it- had to swap the outdoor pcb too

  4. #4
    Join Date
    May 2013
    Location
    SPK
    Posts
    11
    Rep Power
    0

    Re: Panasonics CU-25R --What DCV at terminal of out door unit in normal operatioin .

    Quote Originally Posted by install monkey View Post
    check your wiring isnt crossed between indoor/outdoor
    check indoor fuse spur connections ok, and only switching 240v live and neutral- check wire 3 is thru crimped or terminal block- not switched or any external condensate pump hi pump alarm float isnt wired in

    if unit still shows h11
    then isolate outdoor unit, remove wire 3 (comms line)
    test 2-3 should give a pulsating dc voltage upto 50vdc
    if not check fuses,connection plugs on outdoor boards
    i had a 48-50vdc signal on 1 and appeared to be indoor pcb, after swapping it- had to swap the outdoor pcb too


    So many Thanks.