    compressor suction getting ice frosting
    We have chilled brine water system of minus 30 deg C, when temperature reaching minus 10 deg ice frosting start in expansion valve as well as suction valve. pl help me to resolve the issue
    Sekar
    Jan 2008
    north west
    42
    234
    Re: compressor suction getting ice frosting
    Could be evap flow not sufficient causing liquid refrigerant to stop boiling off before coming back to comp.
    5,667
    Do you mean ice ON the valve or ice IN the valve
    At minus 10C I would expect ice/frost to form ON the valve....this is normal and doesn't need fixing.
    Oct 2009
    Sydney
    water freezes below 0c. there is moisture (water) in the air, around the pipe. you stated its at -10c, so the moisture in the air is freezing onto the outside of the cold components.
    am i missing something??
    Apr 2006
    1,620
    no but the op is, pipe lagging!
    Now in Redvers Sask.
    Jun 2013
    Canada
    1
    It doesn't sound like a serious issue. It happens quite normally at my place. Anyways, it is ideal that you get it checked at a refrigerator repair service center to be on the safe side!
    Apr 2006
    1,620
    the same jenifer from the bc rv forum trying to promote every one to only use general contractors? same location, same name, same empty profile, same age, nearly the same join time. ?