Results 1 to 25 of 25
Thread: New Daikin VRV 4 service manual
25-01-2013, 04:08 PM #1
Hi to all.
I need service manual for new VRV 4.
The DK tech line is not relevant enough (for the moment) to give us informations...!
But next i will try to start one RXYQ10T7Y1B by myself...
Once a service man tried to launch TEST and on step 10 on the new display (?) the system failed to U3.
He tried again and then after it failed to U3-P2.
I think it's a matter of auto charge or something like that...maybe i could disable?
He has calculate the amount of refrigerant like III series upon the lengh and weigh of the liquid lines and he charged the amount.
I will go there with the latest version of vrv checker software (1.53a) but i need advise to lead commissioning as well.
Hope i'll find (nice) RE member to help me ?
cool#9Last edited by cool#9; 26-01-2013 at 11:33 AM.
25-01-2013, 07:13 PM #2
Re: New Daikin VRV 4 service manual
no service manuals on extranet, outdoor installation manual will guide through auto charge, wiring check
25-01-2013, 07:42 PM #3
I have manual, but only RUS.
25-01-2013, 07:52 PM #4
10 point of test start - a unit stop.
U3 in this case - the unit is efficient, but function of automatic search of leak which joins in a mode 2-88 isn't included, and by default not activated.
Cheker won't help, there now new software and a new box for 400 euros.
http://daikin.mcquay.hu/3_Hőszivatty...lthermához.pdf
http://www.daikineurope.com/binaries...524-250456.pdfLast edited by RusBuka; 25-01-2013 at 07:56 PM.
25-01-2013, 08:37 PM #5
25-01-2013, 09:03 PM #6
As you remember to vrv3 and others it was possible to carry out test start having excluded check of amount of *****. Here too there is this function 2-88, it is initially active and it needs to be disconnected, (2-88 to put instead of 0 - 1) and then to refuel system with the help of software. Problem that the software meanwhile isn't available. And your second start the test of a mode showed an error of P2 - extraordinary low pressure in a gas station mode. Advise to open the gas valve)))
that it is advisable to disconnect check of amount of *****
Change of value of the control chosen in a mode 2:
- Execute transition to a mode 2 (for this purpose press the button
BS1 also hold it within not less than 5 seconds),
then choose the necessary control. It becomes
BS2 button pressing.
- Receiving access to value of the chosen control
it is carried out by single pressing of the BS3 button.
- Now the BS2 button serves for a choice demanded
values of the chosen control.
- Having chosen demanded value, set change
current value single pressing of the BS3 button.
- That the system started working in compliance
with the chosen value, press the BS3 button once again.
p.s. I mixed a little, 2-86 control of system on leaks. As I understood periodically supervises ***** volume in system.Last edited by RusBuka; 25-01-2013 at 09:07 PM.
25-01-2013, 10:09 PM #7
Ok i think i understand...
Didn't know mode 2 setting 88 binary set 1 or 0 before, that's why i was confuse.
I've had this kind of problem with the RQYQ series it was sometimes difficult to achieve the TEST...
So i can disable the function and of course check the stop valves and run the service checker with the latest version. I think 1.53c instead of 1.53a.
Many thanks (if i'm wrong please advise!)
Rgds
Cool#9
Sent from my Nexus 7 using Forum RunnerLast edited by cool#9; 25-01-2013 at 10:14 PM.
25-01-2013, 10:20 PM #8
Yes, everything is correct. Just in case steps which are passed in a test mode.
Stages of automatic procedure of trial start:
- "t01": control before start (alignment
pressure)
- "t02": control at cooling start
- "t03": stable condition of cooling
- "t04": connection test
- "t05": check of locking valves
- "t06": check of length of pipes
- "t07": check of quantity of a coolant
- "t08": if [2-88]=0, collecting detailed information
about a coolant
- "t09": coolant pumping
- "t10": block stop
25-01-2013, 10:37 PM #9
Thank you RusBuka i feel stronger than this afternoon...
I'll inform you how i go on
Kind regards
Cool#9
30-01-2013, 05:43 PM #10
Hello
Here i'm back with my new VRV IV.
During the Test the system failed to LC-14 fault as i understand it means pb of communication between main
board and Inverter board.
And on new series they are 2 INV pcb with 2 INV scroll comp i think from 14 to 20 Hp.
I've check the whole wires and connectors, each Pcb has a green led flashing on it...
Local DK tech service ask me to change the 3 pcb's !!!
I think I REALLY NEED THE SERVICE MANUAL ON IT
Awaiting to any suggest
Rgds
Cool#9
Sent from my Nexus 7 using Forum RunnerLast edited by cool#9; 01-02-2013 at 08:06 PM.
30-01-2013, 06:53 PM #11
Excuse dude but I have no service manual. Cheker connected to system? Tried to start without a test mode? What did it show on loading of 1 inverter and current?
INV1 -A1P (X20A, X28A, X40A)
Check here these connections, check wires.Last edited by RusBuka; 30-01-2013 at 07:17 PM.
01-02-2013, 08:14 PM #12
Hi i'm still with my new one!
We've finaly change the inv pcb boards and lead the test run (run fine now)
The new test can last from 3 to 4 hours (!) so...take time while you decide to push the button or disable this function.
Rgds
Cool#9
05-02-2013, 06:35 PM #13
Such long test of system because of function of detection of leaks? If it to leave included?
06-02-2013, 08:20 PM #14
Yes it was with detection of leak first.
Without this function it takes 35 to 55 mn
I've got recording with short test cooling mode and heat also, if someone's interesting of, it's about 1 RXYQ10 and 1 RXYQ12T7Y1B
Ps: sorry Rusbuka i don't have your chiller software as you asked by your PM
Rgds
Cool#9
07-02-2013, 02:27 AM #15
Give me please)
09-02-2013, 10:41 AM #16
VRV IV-Climsud-Marseille FRance.zipHi Rusbuka sorry but a little bit busy at that time
Find attachement.
rgds
cool#9
09-02-2013, 11:03 AM #17
Hi try to make start up check after indor temp is abobe 16-18 degress celsius. I have a similar problem and afyer sisyem was working in heating with U3 on remote check eas completed .
09-02-2013, 11:06 AM #18
For serrvive checker i need almost software v 1.50 or v 1.53
09-02-2013, 11:13 AM #19
Run test on short test was 5 hours long on my vrv 4.
09-02-2013, 03:22 PM #20
Hi Bratosin
You'll need at least 1.53A software and even better with 1.53C
To have a short TEST you will read above that Rusbuka helped me by changing the setting 88 in mode 2.
My opinion is you can start with the short test and after you have to launch the long test (be careful i don't speak about auto-charge!!!).
But if you do that you have to calculate the amount of refrigerant depending on the lengh, size, and combination of indoor, and then charge by the service port (the same as for auto-charge) using the setting 20 in mode 2.
rgds
cool#9
09-02-2013, 09:57 PM #21
Actually never used autocharge function as conditions for this opertion practically weren't. Main thing pumping and filling of evaporators, and working parameters. Only through a cheсker)
p.s. WOW sow interesting logs, many thx )))Last edited by RusBuka; 09-02-2013 at 11:45 PM.
20-06-2013, 07:29 AM #22
Hi everyone,
I am on the processes of buying a VRV unit for my house. There are daikin VRV-III available in the market where I live and VRV 4 will be available in 4-6 weeks. I will use the unit only for cooling purpose for 3 months a year since I have a seperate heating system already installed. Do you think that it will be worth for me to wait for the model? Please note that worth means I need to bear hot weather till mid August. I will appreciate your input.
20-06-2013, 08:01 PM #23
20-06-2013, 09:05 PM #24
And if you are very rich, best choice is MHI, Samsung S or ME
23-06-2013, 01:37 PM #25
Hi me opinion is to wait VRV IV the different is very important I working with VRV III and VRV IV and I can tell you wait