20-05-2013, 08:43 PM #1
mitsi electric 6608?
hi all.
working on few pury systems linked back to g50 then onto sites local network/laptop etc.
g50 showing fault at cond 051 with 6608, noise on mnet. been running for 4 year without fault, all cables screened and correct size, earthed correctly..
any ideas??
thanks
-
20-05-2013, 10:49 PM #2
Re: mitsi electric 6608?
Have you checked the voltage on the comma lines?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-05-2013, 07:14 PM #3
Re: mitsi electric 6608?
yep 29vdc on mnet
-
21-05-2013, 07:15 PM #4
Re: mitsi electric 6608?
Had the same error last week. Turned out I was missing voltage at L3 due to a poor connection in the isolator. Did a full system reset and it cleared the fault.
-
21-05-2013, 07:42 PM #5
Re: mitsi electric 6608?
had it on a hotel- system 4yr old and the comms goes through the power pack before the g50- power pack failing ,thus the comms error
-
21-05-2013, 10:59 PM #6
Re: mitsi electric 6608?
appreciated, off site this week now but will check out mains / power pack etc when back.
-
27-05-2013, 09:46 PM #7
-
28-05-2013, 10:42 AM #8
Re: mitsi electric 6608?
Check the position of the cn41 plugs on the outdoor board.
Cheers