compressor overheating
hi
i have crafft window type air conditioner 24000 btu capacity
it was leaking from service valve
so i degas it
then checked for leaks
and charged it
it works properly
and cooling perfectly
but the compressor is overheating
DSC_2251.jpg
i checked the temperature of
discharge line = 70 C
suction line = 19 C
compressor top cover = 73 C
current = 14 amp
volltage 210 volt
so where is the problem
-
30-04-2013, 08:35 PM #2
Re: compressor overheating
Which refrigerant u r using ?? check the suction & discharge pressure's... How u calculated the length and size of capillary ?
-
30-04-2013, 08:42 PM #3
-
30-04-2013, 08:58 PM #4
Re: compressor overheating
I see no problems with those temperatures.
Also, what type of compressor is it?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-04-2013, 09:13 PM #5
-
30-04-2013, 10:48 PM #6
Re: compressor overheating
You dont tell us all parameters
InDoor temperature
OutDoor temperature
Airflow
SH
if something block air flow or you have jamed air filter)
-
30-04-2013, 11:30 PM #7
Re: compressor overheating
Hi Kefah
Your suction superheat is excessive - 19degC @ 65psi. Current seems a little high - what is the current rated at? Did you charge it by weight with a set of accurate scales or by system pressures. Is it cutting out on a thermal safety because it looks like and old rotary (rotary's run hot). The way it was charged will help with the solution and the current rating. Sorry I don't have a btu converter.
-
01-05-2013, 06:03 AM #8
Re: compressor overheating
Hi kefah, your compressor is rotary. Rotary compressors have designed to work 100c to 120c.73c is normal.
Moideen-Dubai
-
01-05-2013, 08:43 AM #9
-
01-05-2013, 08:45 AM #10
-
01-05-2013, 08:47 AM #11
-
01-05-2013, 10:03 AM #12
Re: compressor overheating
indoor 40 c
outdoor 50 c
I think its not good... Indoor temperature too high, i dont know TROPIC edition unit or not, but indoor too high.Last edited by RusBuka; 01-05-2013 at 10:06 AM.
-
01-05-2013, 10:45 AM #13
-
01-05-2013, 12:24 PM #14
Re: compressor overheating
Its normal.
-
01-05-2013, 12:37 PM #15
-
01-05-2013, 01:22 PM #16
Re: compressor overheating
Hi Kefah
Moideen has given temps for comp. Why do you think the compressor is overheating?. Will it pull the room down to a reasonable temp or is it cutting out on a compressor thermal safety (klixon)? there may be no problem apart from a high initial load for the unit.
-
01-05-2013, 07:29 PM #17
-
01-05-2013, 09:03 PM #18
Re: compressor overheating
Compressor case temperature is within limits.
System can only be analysed when it had reached design conditions, during pulldown readings will often appear strange.
Also, have a read of this....
http://www.parker.com/parker/jsp/doc...0048021dacRCRD
Lots more technical information available here if you want it...
http://www.parker.com/portal/site/PA...ype=literatureLast edited by Brian_UK; 01-05-2013 at 10:52 PM.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
04-05-2013, 09:44 AM #19
-
23-05-2013, 07:59 PM #20
Re: compressor overheating
dear Kifah,, I think there is nothing wrong with your unit. it is running with normal conditions. do not worry, rotary comp.s usually run hot
regards
-