Thread: Sporlan TEV.
    70
    4,700
    47
    Sporlan TEV.
    I fitted a replacement power-head the other day, which had note with it reading.
    VN power-head is a non-migrating charge that may be substituted for a Hydraulic power head.
    Am I being thick?
    What do they mean?
    3,853
    Re: Sporlan TEV.
    Think it means the charge in the bulb wont migrate to the bellows if that is the colder place, which can then result in insufficient pressure to operate the valve. Not so sure about the hydraulic part tough!
    70
    4,700
    47
    Re: Sporlan TEV.
    Yes my friend you are correct on that part.
    It's the Hydraulic part that I am not sure about.
    Feb 2013
    Rochester, NY
    Re: Sporlan TEV.
    They make heads full of liquid? That would scare me a little.
    manchester
    5,639
    Re: Sporlan TEV.
    Hydraulic Elements — These thermostatic elements are
    specially designed double diaphragm elements which provide a pressure limiting feature without the problems associated with charge migration from the bulb when the element
    becomes cooler than the bulb. The hydraulic element is
    often used on chillers which require a TEV with an MOP
    type charge, but experience problems with charge migration caused by cold ambient temperatures. For additional
    information on the hydraulic element, contact the Sporlan
    Division of Parker.
    sourced from sporlans website
    http://sporlanonline.com/literature-...ansion-valves/
    70
    4,700
    47
    Re: Sporlan TEV.
    Thanks IM.
    I would of given you Reps but I have to spread the love first.
