    Some Mitsubishi Mr Slim units have an activated charcoal filter fitted which soak up chlorines and contamanents to allow you to re-use existing R22 pipework when replacing an old system.
    Does anyone know if such filters are available as a seperate component?

    Simon.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: R22 to R410a

    I don't think so Simon, they are built into the invertor series only and I believe are a one shot item. Probably large enough to clean up the oil from the maximum pipe run allowance plus a bit for normal running.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2002
    Location
    Manchester UK city of rain
    Age
    51
    Posts
    37
    Rep Power
    0

    Re: R22 to R410a

    Do you know if its possible by others mean of cleaning R22 pipework for a new 410a unit? In the old days it would have been flushed with R11, is there a replacement?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: R22 to R410a

    There are chemical cleaners available for the job but to be honest I think that the cost and time involved with them would encourage you to renew the pipework.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    57
    Posts
    164
    Rep Power
    19

    Re: R22 to R410a

    Hi Guys.
    Mitsubishi use there own oil alkylbenzene Type which is isoluble in refrigerant and can be used in older systems so the R22 pipe work can be used without worry No need to fit any driers or clean the pipework or so they Say in the latest Tech Bulletin from Japan. Have never used it myself so can't comment.
    PS
    Don't tell anybody I've seen the latest Japanese tech bulletin it's a secret
    Cya
    T

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: R22 to R410a

    Also, the comparable pipe size has reduced with R410a (suction line smaller) so oil return issues may be something to consider if you want to re-use old R22 piping.

  7. #7
    Join Date
    Aug 2005
    Location
    New Zealand
    Age
    55
    Posts
    7
    Rep Power
    0

    Re: R22 to R410a

    im not sure if it is available were you are , but we use R141B whitch is a very similar product to r11 but without the ozone depleting characteristics, it works very well on removing scale and oil residue, also reusing original pipework be carefull that thinner wall copper tube wasnt usaed in original installs , as new certs are being inforced over here for the thicker walled 410 certified pipe.

  8. #8
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: R22 to R410a

    Quote Originally Posted by paulcollis
    but we use R141B whitch is a very similar product to r11 but without the ozone depleting characteristics,
    Not so sure about that........

    R141b s a HCFC. All Chlorinated gases are severly restricted or banned in the EU.

    R141b weighs in with an ODP of 0.11, twice that of R22.

    It's use as a temporary flushing agent would be legally doubtful in this part of the world and questionable best practice.. Once used it becomes a Hazardous Waste and you then governed by all sorts of disposal licenses.
    ________
    fake weed
    Last edited by Argus; 07-02-2011 at 08:29 AM.

  9. #9
    Join Date
    Aug 2005
    Location
    New Zealand
    Age
    55
    Posts
    7
    Rep Power
    0

    Re: R22 to R410a

    We have used this system over here for a number of years, we have a fully sealed flushing system so there is no release of by products to the atmosphere, we then send the 141 through a series of filters, one of whitch is especially designed to remove any oil and acid residue, this inturn enables the flushing agent to be reused several times, to ensure the system is clean, once this is finished, we have a refrigerant disposal depot were for a small fee they breakdown the agent and dispose of it in an enviromentaly safe manner.

  10. #10
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: R22 to R410a

    Quote Originally Posted by paulcollis
    We have used this system over here for a number of years,

    Still, it's illegal in the EU. Any HCFC use as a solvent is banned.

    .
    ________
    teen vid
    Last edited by Argus; 07-02-2011 at 08:29 AM.

  11. #11
    Join Date
    Mar 2002
    Location
    Sydney Australia :D
    Age
    53
    Posts
    47
    Rep Power
    0

    Re: R22 to R410a

    The main factor to consider is the fact that 410 runs at much higher pressure than 22 & by law requires a thicker copper pipe. Those regulations are for safety reasons. Imagine what would happen if the pipe split while it was running in heating....WOW !!!
    :cool: Do the job once & do it right. :cool:

  12. #12
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,453
    Rep Power
    41

    Re: R22 to R410a

    Simon,

    Did you have any luck cleaning your pipework, i'm looking at a job involving reusing existing pipework and was curious if you found any means to do so?

    Al

  13. #13
    Join Date
    May 2001
    Location
    North Wales
    Posts
    47
    Rep Power
    0

    Re: R22 to R410a

    By the time you spent on this web site asking questions you could have changed out all the pipe work…. Have a nice day mate!

Similar Threads

  1. Copper pipe for Mitsubishi R410a Models
    By Chris2005 in forum Air Conditioning
    Replies: 5
    Last Post: 26-01-2008, 12:30 AM
  2. R410A split min and max line temps
    By smileypete in forum Domestic
    Replies: 1
    Last Post: 17-11-2005, 10:38 PM
  3. Is this tube OK for R410A?
    By smileypete in forum Air Conditioning
    Replies: 12
    Last Post: 04-08-2005, 09:33 PM
  4. R410A captube sizing for 2.5 bar / 35 psi pressure drop
    By DaBit in forum Technical Speculations
    Replies: 10
    Last Post: 27-11-2003, 09:05 AM
  5. R410a
    By Nobby in forum Refrigerants
    Replies: 3
    Last Post: 02-07-2002, 01:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •