Results 1 to 10 of 10
12-03-2013, 07:41 AM #1
humidity- damaged chilled water insulation
IS IT CORRECT,
The reheat coil of FAHU does not reduce the humidity, but increase the sensible load and maintaining the relative humidity by increasing the dry bulb. Same like slightly increasing the dew point temperature also.
I don’t know whether my question is dumb, when increasing the dew point, increasing the possibility of condensing the water in side the air conditioned area and the chance to damage the chilled water insulation. Right now I am facing a humidity issues, it damaged entire 4 year old chilled water insulation and water is dripping everywhere. Location is island, high humid area. Maximum ambient will reach 52c and some time wet bulb will go above30c.
During the first inspection, I found the FAHU Johnson controller FX15 setting is 80%RH and leaving temp set point24c. Re-stetted to 50%RH and 22c.we are going to replace the insulation.
Your any valuable comments highly appreciated.
Moideen-dubai
12-03-2013, 12:08 PM #2
Re: humidity- damaged chilled water insulation
The reheat coil does change the rh. The chilled water coil air off is supposed to be set for a condition that when reheated/ mixed the humidity is of the required rh level to maintain the conditioned space. water running everywhere is a sign of poor insulation or blocked drains if before the reheat or if after then poor insulation or reheat failure/ incorrect setting. The dewpoint of the equipment surfaces in tropical conditions can be quite high.
Hope this helps but further information would be required for any more depthQuidvis Recte Factum Quamvis Humile Praeclarum.
12-03-2013, 12:35 PM #3
Thanks trash, yes today I have informed site technicians to record the RH level one week: And also planning to fix additional heater coil for the same FAHU to improve the RH level. Or else by fixing low static fan coil units it works only to decrease more humidity and not more cooling effect.
14-03-2013, 06:27 AM #4
Yes, when you intoduce a reheat coil, the DBT increases. This can be well visualized if you imagine a pschyrometric chart. The point moves to the right (SENSIBLE HEATING). The RH is lowered, DBT is increased.
Dew point occours when DBT and WBT are same. So, basically you cannot increase the dew point, its the ambient temprature determining what the DPT is! The reason behing condensatin is two..
1. Insulation thickness is not sufficient / damaged
2. Outside air (ambient) happens to enter the conditioned space in high volume... This can cause condensation on the walls, ceilings etc...
Its always suggested to keep the building in positive pressure to achive this. Is the building too old, may the theres too much of exhaust happening in the air system!
15-03-2013, 07:55 AM #5
Hi nevin,
RH and absolute humidity is deferent terms. It cannot consider as single term. Yes when increase the temperature RH will maintain, but the same amount of moisture (absolute humidity) will remain after the reheating, I am talking about the dpt condition after the cooling coil. Recheck your chart, when increase the sensible heat, also increasing the dew point temperature.
30-04-2013, 11:29 AM #6
Yes, absolute humidity will remain the same, but RH will decrease!.
To decrease absolute humidity, introduce cooling coils and make sure condensation occours at the coil!!.
This will make both RH and absolute humidity to decrease, as in the case of an air conditioner.
N.B
I wasn't reffering to absolute humidity in any of my posts mentioned above,
Hi nevin,
RH and absolute humidity is deferent termsLast edited by nevinjohn; 30-04-2013 at 12:05 PM.
30-04-2013, 02:54 PM #7
In order to achieve 50% RH in the room, the air temperature leaving the coil needs to be about 11K/20F below the room temperature.
01-05-2013, 02:56 PM #8
02-05-2013, 05:27 AM #9
02-05-2013, 12:48 PM #10