    5/16 liquid line left in place instead of replacing with 3/8



    Hello all, I'm a homeowner who just had installed a Rheem model 13AJN 13 SEER condensing unit and evap coil.

    Here's the issue- our contract says he would replace the liquid line with a new 3/8 inch run. When I got home I noticed my original 5/16 run was still in place, he just soldered onto the 3/8 at both coils. BTW- the run is approx 25 feet.

    I called him on this. He said he checked the pressure and it was fine. I figured it was ok. But I wanted to check this with some experts to confirm.

    Do you guys think this is appropriate? Or was a short-cut taken?
    Further more- if he didn't replace it, aren't I entitled to some reimbursement?

    I care less about the money than having the job done right. The lines to both coils are 3/8, so it would seem that the system is engineered for a 3/8 liquid line, right?

    Thanks in advance for any clarity you can provide.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 5/16 liquid line left in place instead of replacing with 3/8

    http://www.manualowl.com/swfviewer/v...lsVisible=true
    page 24 mentions liq line size dependant on length of run and whether outdoor is above or below the indoor

  3. #3
    Join Date
    Apr 2013
    Location
    USA
    Posts
    4
    Rep Power
    0

    Re: 5/16 liquid line left in place instead of replacing with 3/8

    Quote Originally Posted by narkom View Post
    To get an expert help you should provide the full model identification so we can see its NOMINAL COOLING CAPACITY.
    The evap is model number CFL-HM3621CC.
    The condensor is model number 13AJN030.

    Thanks!

  4. #4
    Join Date
    Apr 2013
    Location
    USA
    Posts
    4
    Rep Power
    0

    Re: 5/16 liquid line left in place instead of replacing with 3/8

    Quote Originally Posted by install monkey View Post
    http://www.manualowl.com/swfviewer/v...lsVisible=true
    page 24 mentions liq line size dependant on length of run and whether outdoor is above or below the indoor
    Install Monkey- attached is the relevant section you suggested. I hi-lited what I think is applies to me- but I'm not sure how to interpret it. Any thoughts?

    line size.jpg

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 5/16 liquid line left in place instead of replacing with 3/8

    it states that for an outdoor unit above the evap, with a piperun of less than 25ft 5/16 is ok, also 5/16 is suitable for upto 150ft!!!- it does say not applicable in a heat pump.
    Quote Originally Posted by harpert1 View Post
    Install Monkey- attached is the relevant section you suggested. I hi-lited what I think is applies to me- but I'm not sure how to interpret it. Any thoughts?

    line size.jpg

  6. #6
    Join Date
    Apr 2013
    Location
    USA
    Posts
    4
    Rep Power
    0

    Re: 5/16 liquid line left in place instead of replacing with 3/8

    Quote Originally Posted by install monkey View Post
    it states that for an outdoor unit above the evap, with a piperun of less than 25ft 5/16 is ok, also 5/16 is suitable for upto 150ft!!!- it does say not applicable in a heat pump.
    OK, great. Sounds like the engineering is ok. So now the only issue is should I ask for reimbursement based on that line not being replaced as stated in the contract. Any idea what the material and labor on 25 feet of line replacement would be?

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 5/16 liquid line left in place instead of replacing with 3/8

    not much labour on running the pipe, uk cost for a 15 m coil of 3/8 pipe £17 and if majority of the pipework is outside or in a loft area then its a quick job, few hrs labour for pumping down the system running a new line,pressure test,vac and reinstate system.

    worth a try for compensation