    new guy need help with carrier unit



    hi,i am new here but i really need some help.
    i have a problem with carrier ultra xtc unit.
    the problem is when the unit is running start/stop mode and reach setpoint, it is cutting of,but the actual box temp. aprox.10-12 deg. higher.
    exm. set temp 0 deg ,unit cut of 0 deg.,but actually the box temp 12 deg
    please help
    tx



  2. #2
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: new guy need help with carrier unit

    Sounds like the sensor is out of calibration, out of it's correct position, covered by something insulting. Or the sensor is fine & the controller is set wrong or faulty.

    Can't help further than that as I don't know the equipment.

  3. #3
    Join Date
    May 2012
    Location
    AUSTRALIA
    Age
    34
    Posts
    51
    Rep Power
    13

    Re: new guy need help with carrier unit

    put the sensor in the return air duct and see what happens , any what type of thermostat is it.

  4. #4
    Join Date
    Apr 2013
    Location
    us
    Posts
    3
    Rep Power
    0

    Re: new guy need help with carrier unit

    sometimes the unit not cutting of just start heating then cooling few times before cutting of.
    it can be related to a same problem?
    it is running on the old 03.03.00 software
    it can be also a problem?
    thanks