    Atlas copco dryer



    Hi
    got a dryer that has hgbv solenoid on dew point was going too high,was advised to remove valve and dp would stay at 3.9oc which it has. Problem is unit tripping on high pressure occasionally when you put valve back on unit ok for while and then dp starts to rise .any advise woul be welcome , thanks



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Atlas copco dryer

    Wonder if system has been overcharged with refrigerant to the point it backs up in the condenser and causes the hp switch to trip. Assuming the switch is tripping at the correct pressure.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Atlas copco dryer

    Do not change the unit, simply recover the refrigerant, replace drier, vacuum and recharge.
    I had the same problem a few times and this prosidure seemed to correct everything.

  4. #4
    Join Date
    Sep 2010
    Location
    manchester
    Age
    52
    Posts
    47
    Rep Power
    0

    Re: Atlas copco dryer

    Thanks for reply guys