    Daikin RYP board replacement



    The patient - Daikin RYP 100 L7W1

    Issue - needs a capacity setting adapter to commission the new board?????

    Never come across this before

    Anyone care to enlighten me as to the why and where of this "adapter"

    Thanks chaps


    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Daikin RYP board replacement

    When the unit leaves the factory, it has the 'Capacity' setting installed in the EEPROM via software, as the outdoor boards fit multiple size units.

    If you replace the outdoor board, or indeed the indoor pcb, you need the capacity setting resister to tell it what capacity it is supposed to work at, i.e. 7.1kW, 10kW, 12kW, 14kW

    It is a small resistor that just plugs onto the pcb.

    Whoever sold you the pcb should have advised that the resistor was required

  3. #3
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Daikin RYP board replacement

    Thanks Frank

    Couldn't buy through a more direct source as company policy don't like me sourcing through non account stockists.

    Well they'll just have to keep using the "leccy" heaters until it gets here LOL

    Cheers again
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin RYP board replacement

    Trash,

    You should have receiced instruction with the PCB, there are 3 x jumpers on the new board that may also need to be cut and 2 x connectors that must be removed form original PCB and refitted to the replacement.

    Jumpers:
    JH = Compressor type
    J4 = Voltage selection
    J5 = Cooling only / heat pump
    Last edited by VRVIII; 26-02-2013 at 05:23 PM.

  5. #5
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Daikin RYP board replacement

    Yup got them
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  6. #6
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Daikin RYP board replacement

    Although in the case of JH what is so different about Daikins own comp so as to require that jumper..........you any ideas on that VRVIII

    Thanks

    Trash
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  7. #7
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Daikin RYP board replacement

    You can prob use the old one from board taken out , then set dip switches to relevant settings , if in doubt ring daikin tech @01932 879 000 uk