    Flushing agent..Endo flush or a-gas stuff



    Need to flush out a system after a severe burnout, i have it on good advice that endoflush wont evaporate under vaccum, and i cant be dealing with some of that stuck in the system. Any guidance? Looking for something i can get out and then ensure its out after a good vac

    Water chiller 1 + 2 n half inch pipework then a condenser 4mx2m in size...so fair amount of pipework.

    thanks x



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,024
    Rep Power
    36

    Re: Flushing agent..Endo flush or a-gas stuff

    Have used the The stuff from NRS - AK Flush.

    It evaporated in the tin I collected it in when the lid was off so guess if you are worried about it getting trapped then a vac should sort it out (but not get the crud out though!).

    Cheers,
    Andy,
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Flushing agent..Endo flush or a-gas stuff

    Thats the stuff...so if it wont get the crud out then......what will it do

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,024
    Rep Power
    36

    Re: Flushing agent..Endo flush or a-gas stuff

    Ha, just shift it all round to the same I suppose!

    Endoflush not evaporating? Says who? Not checked myself but if it is a solvent based chemical which I imagine it must be to clean stuff out then surley it would evaporate but perhaps slowly.
    Time Jon put a video up on you tube to settle the arguement.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,453
    Rep Power
    41

    Re: Flushing agent..Endo flush or a-gas stuff

    Have used endo flush and it wouldn't shift under vac, was 3 years ago so maybe composition has changed, was told by wholesaler it wouldn't evap either, had to drill shraeder into pipes to physically drain it, hence it didn't shift under vac.

    alec
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Flushing agent..Endo flush or a-gas stuff

    Best flush was with Trichlorofluoromethane (R11) but with an ODP of 1.0 in comparison to R22 of 0.055 you can see the problem!

    Endoflush is basically Ethyl Di Glycol (used in brake fluid, print cleaners, paints and wood stains etc) it is a fluid flush and then requires removal. It does not evaporate easily and is usually purged from system with nitrogen.

    Before committing to a system flush you need to ascertain how bad your contamination really is. Sludges and carbon deposits are the target for flushing deposits.

    A new refrigerant charge, oil changes and burn out cores with after clean monitoring usually suffices.
    I love the smell of Ammonia in the morning!

  7. #7
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Flushing agent..Endo flush or a-gas stuff

    I`ve used Endoflush and purge it out with dry compressed air (put through a dessicant dryer to give a DP of around -60c). You`ll need a decent compressor and reciever though so it`s only practical on a system which would warrant spending time setting it up. Then purge the air with nitrogen. I do this as the price of nitrogen is exepensive enough without blowing it through pipework to remove Endoflush etc. With dry compressed air you could leave it on all day as the customer is paying for the power used. Youll only use the ntrogen for the final purge.

  8. #8
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Flushing agent..Endo flush or a-gas stuff

    Optimized-DSCF0136.JPGOptimized-DSCF0137.jpg

    Just a couple of photos, sludge and soot in the condenser too!

    I've got a company coming in to flush the entire system, apparently they use R22, the system takes 54kg and as an estimation the company told me they use 4x the rated charge to flush it. I'll report back on RE when it gets done. Decided it wasn't worth the risk using endoflush etc...

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Flushing agent..Endo flush or a-gas stuff

    Mostly found in Oxfordshire, UK :)

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Flushing agent..Endo flush or a-gas stuff

    I have in the past used all the above ideas, all sorts of effectively crap removal products, great for cleaning systems etc., getting the residual effects out systems is the real problem. No real answers apart from truck loads of suction clean up driers and liquid line driers and megga oil changes and oil testing. Sporlan do a really effective suction clean up filtering system.