    Noisy Daikin in Heating Mode.



    Hello has anyone encountered a problem with a Daikin heat pump split a/c unit that appears to work happily in cooling mode, but when in Heat mode it's ineffective and the compressor sounds like a bag of spanners falling down the stairs.
    Its not short of Gas nor is it the 4 way valve, Daikin Tech suggest a new compressor and exp. valve but this seems a bit excessive.

    Any hints cheers.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Noisy Daikin in Heating Mode.

    hi dave
    is the indoor fan running full speed ? if not the systems psig could be getting very high, = sedgy

  3. #3
    Join Date
    Jan 2009
    Location
    United Kingdom
    Posts
    11
    Rep Power
    0

    Re: Noisy Daikin in Heating Mode.

    Cheers Sedgy,
    fan speed fine, it shows signs of low refrigerant as very poor Refrigeration Effect although in this case it aint Heating. When I check the indoor unit coil temp this is very low and the heat is lost very quickly in the coil.
    Dave.

  4. #4
    Join Date
    Mar 2005
    Location
    New Zealand
    Age
    43
    Posts
    64
    Rep Power
    20

    Re: Noisy Daikin in Heating Mode.

    Need to know system pressures really, then we can work out if its a high or low pressure problem. If a compressor runs ok in cooling then why wouldn't it in heating? The actual operating pressures at the compressor are very similar in heating or cooling.